[RE-wrenches] closets and working space

AE Solar autonomousenergies at gmail.com
Thu Jun 2 12:28:51 PDT 2016


Ha thanks. I figured there was something about that situation that wasn't
right. The main panel is already located there. Maybe I will just add a
partition into the closet (it's probably 8' wide) so that half can be
designated 'coat closet' and the other half designated 'utility closet'?

On Tuesday, May 31, 2016, August Goers <august at luminalt.com> wrote:

> Hi Adam,
>
>
>
> Check out “NEC 240.24(D) Not in Vicinity of Easily Ignitible Material.
> Overcurrent devices shall not be located in the vicinity of easily
> ignitable material, such as in clothes closets.”
>
>
>
> -August
>
> Luminalt
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org
> <javascript:_e(%7B%7D,'cvml','re-wrenches-bounces at lists.re-wrenches.org');>]
> *On Behalf Of *AE Solar
> *Sent:* Monday, May 30, 2016 5:08 PM
> *To:* RE-wrenches
> *Subject:* [RE-wrenches] closets and working space
>
>
>
> Hey Wrenches,
>
> We'd like to put a combo panel in a coat closet (its shallow and wide)
> right next to the existing panel. With the doors open (they are pocket
> doors) it is fine with working space requirements. I know the AHJ will have
> the ultimate say and am checkin in with them as well but wondering if
> anyone has thoughts on why that could be a bad idea?
>
> Thanks
>
> Adam
>
>
>


-- 
Adam Katzman
Autonomous Energies
PO Box 1245
Kingston, NY 12402
www.autonomousenergies.com
(518) 567-1468