[RE-wrenches] Off-grid generator update?
Dave
dave at independentpowerllc.com
Thu May 5 11:21:12 PDT 2016
For off grid systems with back up charging powered by diesel, what is the best fuel treatment to add to a 275 gallon diesel fuel tank that is sitting about half full?
The summer use of the diesel gen is typically very low until November on a properly sized PV system here in Vermont.
Thanks,
Dave
David Palumbo
Independent Power LLC
462 Solar Way Drive
Hyde Park, VT 05655
802-371-8678 cell
802-888-4917 home
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Chris Mason
Sent: Thursday, May 05, 2016 12:49 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Off-grid generator update?
This is the major disadvantage of diesel over propane.
Diesel can be corrupted with bacteria, water through condensation and algae. Fuel polishing is the process to clean the diesel and remove the contaminants, the equipment is expensive so it is normally done as a service.
If the fuel goes bad, it can ruin the injectors and pump, requiring a very expensive service.
Propane dissipates in the engine, and propane stores indefinitely without degradation.
http://criticalfueltech.com/faq.html
On Thu, May 5, 2016 at 10:02 AM, jay <jay.peltz at gmail.com> wrote:
Question to all the generator techs out there.
I’ve always been told that you don’t want a diesel to be sitting for long periods. Fuel can go bad, all that sort of thing.
Vs propane which doesn’t care.
Is that true?
Or in mild climates will a monthly must run be OK?
Thanks
jay
On May 5, 2016, at 6:13 AM, Mac Lewis <maclewis1 at gmail.com> wrote:
Chris,
Yes, this is a good point. The QT series from Generac is a great machine and pricing is better than any other machine in that size that I've seen. Is there an off-grid warranty on the QT series?
On Thu, May 5, 2016 at 3:14 AM, Chris Mason <cometenergysystems at gmail.com> wrote:
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
--
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician
www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160505/cae778e4/attachment-0003.html>
More information about the RE-wrenches
mailing list