[RE-wrenches] Generac EcoGen problem

Rich Nicol rich at solartechvt.com
Fri Apr 29 10:45:48 PDT 2016


I've seen a number of Eco Gen's go with no issues for a long time and 2
others blow all the oil out just as Drake noted. Rather worrisome!
Rich

-----Original Message-----
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
Behalf Of Drake
Sent: Friday, April 29, 2016 1:18 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Generac EcoGen problem

The one and only EcoGen I installed blew out its oil in within the first
couple hours of running. 
It severely damaged the engine. Generac did the service and ultimately
replaced the unit. It had something to do with the two reservoirs and the
hoses.


At 11:59 AM 4/29/2016, you wrote:
>Wrenches,
>
>I service an off grid home that has an EcoGen 6kW Model 58181 LP gen 
>with a Serial Number of 8301854. It has 1,175 hrs on it during 2-1/2 
>years of service.
>
>.         It appears that the crankcase is 
>filling with excessive amounts of oil.
>.         There was a Generac Service Bulletin 
>in July of 2013 which predates this generators Serial Number. This 
>bulletin alerted the possibility of excessive oil in the crankcase due 
>to "incorrect routing of the pulse pump hoses".
>.         From the pictures on the service 
>bulletin (and with the SN being higher) it looks like the generator in 
>question has properly routed hoses. See photo attached if you are 
>familiar with this problem.
>.         There is an extra oil reservoir on 
>these units. The engine takes 1.7 quarts and the reservoir takes 4.2
Quarts.
>.         I last changed the oil (and properly 
>filled both engine and reservoir) at 1,124 hours
>.         Now at 1,175 hrs the generator runs 
>very roughly and blows lots of oily smelling blue/grey smoke. Most of 
>the oil is gone from the reservoir so it's pretty obvious that the oil 
>has flooded into the crankcase.
>.         If the Pulse Pump hoses are routed 
>correctly and I'd say they are since the SN is later than the 
>recognized problem AND the fact this generator ran great for over 1,100 
>hours then maybe is the pulse pump itself is bad?
>.         I wanted to run this by this list 
>before talking to Generac because I know there are a number of wrenches 
>whom have experience with the EcoGen.
>.         Can I simply just drain the oil and 
>only refill the 1.7 Qts in the engine and run the unit?
>
>Thanks for your time,
>
>David Palumbo
>Independent Power LLC
>462 Solar Way Drive
>Hyde Park, VT 05655
>802-371-8678 cell
>802-888-4917 home
>
>
>_______________________________________________
>List sponsored by Redwood Alliance
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change listserver email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.
>html
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out or update participant bios:
>www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org






More information about the RE-wrenches mailing list