[RE-wrenches] 2014 NEC 705.22 disconnect for inverter capable of being locked
Solar
dahlsolar at gmail.com
Thu Apr 28 19:59:00 PDT 2016
So an AC disconnect in the inverter output between the inverter and panel or utility disconnect if required doesn't work for him or her? The locking provision is always in place on a standard AC disconnect.
Jesse Dahl
NABCEP PV Installation Professional
IBEW Local 292 - Electrician
Electrical/Solar PV Instructor - HCC
Sent from my iPhone
> On Apr 28, 2016, at 5:58 PM, jay <jay.peltz at gmail.com> wrote:
>
> HI August,
>
> I guess my question is.
> Are they asking for a lockout AC disconnect on a AC circuit IE from the AC panel?
> or
> are they asking for a lockout from the inverter AC at the inverter?
>
> thanks
> jay
>
> peltz power
>
>
>> On Apr 28, 2016, at 3:11 PM, August Goers <august at luminalt.com> wrote:
>>
>> Hi Wrenches,
>>
>> We have a particular plan checker who wants us to provide a lockable AC disconnect for our inverter output circuit. His particular issue is that he wants the locking mechanism to be installed and on site. Here is a little NEC background info:
>>
>> 2014 NEC 705.22 Disconnect Device
>> The disconnecting means for ungrounded conductors shall consist of a manually or power operable switch(es) or circuit breaker(s) with the following features:
>> (1) Located where readily accessible
>> (2) Externally operable without exposing the operator to contact with live parts and, if power operable, of a type that could be opened by hand in the event of a power-supply failure
>> (3) Plainly indicating whether in the open (off) or closed (on) position
>> (4) Having ratings not less than the load to be carried and the fault current to be interrupted. For disconnect equipment energized from both sides, a marking shall be provided to indicate that all contacts of the disconnect equipment might be energized.
>> Informational Note to (4): In parallel generation systems, some equipment, including knife blade switches and fuses, is likely to be energized from both directions. See 240.40.
>> (5) Simultaneous disconnect of all ungrounded conductors of the circuit
>> (6) Capable of being locked in the open (off) position
>>
>> NEC 110.25 Lockable Disconnecting Means:
>> Where a disconnecting means is required to be lockable open elsewhere in this Code, it shall be capable of being locked in the open position. The provisions for locking shall remain in place with or without the lock installed.
>>
>> Many times we are using a standard back-fed circuit breaker to comply with 705.22. Then we can supply a handle padlock attachment such as the one shown for Square D:
>>
>> http://static.schneider-electric.us/assets/pdf/retail/QO-and-Homeline-Accessories.pdf
>>
>> Does anyone else have experience installing these breaker handle padlock attachments? My concern is whether we can find them for all of the old types of breakers that we have to deal with. Also, our plan checker is requiring that this handle padlock attachment accessory is installed at the time of our inspection. Is anyone else dealing with similar issues?
>>
>> Best,
>>
>> August
>> Luminalt
>>
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160428/f7bc1e3b/attachment-0002.html>
More information about the RE-wrenches
mailing list