What about building a 30 vdc system (5 x 6v batteries in series) and
adjust the settings on a Midnite Classic to work with that? How tight
does the 30 vdc output need to be?
On inverters, I've had trouble with the Suresine, basically not working
with GFCI outlets.
I keep trying different models of GFCIs, but they keep randomly tripping
on 2 different systems.
Morningstar's list of "approved" GFCIs doesn't list any currently
manufactured models, while calls to their tech support yields "Oh, that
shouldn't be a problem, it should work with all GFCIs..."
Way too many free trips out trying to fix this, so I may have to abandon
GFCI protection, or replace the inverters.
My suggestion for that small load: Exeltech 125. Better than grid
waveform, and I recently pulled one out of corroded outdoor enclosure
almost 15 years old: it looked terrible, but was still working fine. It
would also be lower cost and fit in a smaller enclosure.
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 3/28/2016 2:24 PM, Dan Fink wrote:
> Hi William;
> 30VDC is kind of odd, but 36VDC is common. The folks at Solar
> Converters might be able to fix you up with a custom one, or perhaps
> 36V is within the sat unit's input range.
> As for the inverter, I've never gone wrong with the Morningstar
> SureSine. Slick little unit.
>
> Dan Fink
> Adjunct Professor of Solar Energy Technology, Ecotech Institute
> IREC Certified Instructor™ for:
> ~ PV Installation Professional
> ~ Small Wind Installer
> Executive Director, Buckville Energy
> NABCEP Registered Continuing Education Providers™
> 970.672.4342 <tel:970.672.4342>
>
>
> On Mon, Mar 28, 2016 at 1:44 PM, William Miller
> <william at millersolar.com <mailto:william at millersolar.com>> wrote:
>
> Friends:
>
> I am designing a satellite data interface for a large off-grid
> system for a state highway department facility. We will be using
> the Outback Optics data capabilities along with equipment
> manufactured by Control by Web.
>
> I’d like to run the satellite system on a battery power source so
> I can hope to use it when we need it most, when the power is
> down. We have a separate 24 volt battery bank remaining from a
> previous generator control system. The satellite system operates
> on 30 VDC at 2 amps.
>
> My first choice is to find a DC to DC converter from nominal 24
> volts. Do any of you know of one that you could recommend?
>
> My second choice is to use a small inverter. Can anyone suggest
> one at this small wattage? I don’t know how good the power supply
> is at rejecting waveform distortion so I presume an inverter needs
> to be somewhat close to a sine wave.
>
> Thanks in advance.
>
> William Miller
>
> Gradient Cap_mini
> Lic 773985
> millersolar.com <http://www.millersolar.com/>
> 805-438-5600 <tel:805-438-5600>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160328/6c14d099/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1460 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160328/6c14d099/attachment-0002.jpe>
More information about the RE-wrenches
mailing list