[RE-wrenches] Wire locator
Chris Mason
cometenergysystems at gmail.com
Mon Mar 14 13:59:01 PDT 2016
We have a Schonstedt unit, works very well for electrical services. There
has to be current in the cable to see it. Otherwise you can find data
cables and dead electrical cables by injecting a signal using the signal
generator, either by induction or direct connection.
It can find a service very accurately and give you the depth. However, it
takes some practice as you can get fooled by stray currents and water
pipes. It's nicely made and robust.
Price is a bit more than you were expecting, if memory serves me right. You
can rent for one-offs.
www.schonstedt.com
On Mon, Mar 14, 2016 at 3:36 PM, Kristopher Schmid <solman at legacysolar.com>
wrote:
> Hi Wrenches,
>
> Do any of you use a underground wire locating device? If so, can you
> recommend a brand? I've seen them for $50 and $2,500. Reply off list,
> please.
>
> Thanks,
> Kris
>
> --
> Shine On!
>
> Kris Schmid
> Legacy Solar, LLC
> 864 Clam Falls Trail
> Frederic, WI 54837
> www.legacysolar.com
> 715-653-4295
> NABCEP Certified PV Installer
> Licensed Wisconsin Master Electrician
> BSEE
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
--
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician
www.cometsolar.com <http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160314/59c4dd03/attachment-0002.html>
More information about the RE-wrenches
mailing list