[RE-wrenches] fusing requirement for 4 strings run to a Inverter with 2 MPPT's

Jerry Shafer jerrysgarage01 at gmail.com
Wed Jan 27 10:21:16 PST 2016


Regarding the primo we just installed 5 at a location and used the midnite
with the switch, (mnpv6 disco) its the only way on this inverter to perform
any testing. With all the issues it helped out a great deal.
Jerry
On Jan 27, 2016 4:09 AM, "Allen Frishman" <amfrish at aeonsolar.com> wrote:

> Wrenchers,
> What is the requirement for fusing 2 strings per MPPT?     Specifically
> for an inverter like the Fronius Primo that has no integrated fuses.    If
> you run 2 strings to each MPPT do you need to fuse each string?    In this
> case there is a total of 4 strings which would need to be fused if using a
> single mppt.
>
> If the home runs are run in separate conduits from the array to limit the
> strings in the conduit to 2 per you still have all 4 strings together in
> the inverter.
>
> All thoughts and feedback are appreciated.
>
> *Al Frishman*
> AeonSolar
>
> *(917) 699-6641 <%28917%29%20699-6641> - cell*
> *(888) 460-2867 <%28888%29%20460-2867>*
> *www.aeonsolar.com <http://www.aeonsolar.com/>*
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160127/2370bd56/attachment-0002.html>


More information about the RE-wrenches mailing list