[RE-wrenches] Trojan L-16 charge settings
Howie Michaelson
howie at suncatchervt.com
Mon Jan 18 20:49:25 PST 2016
William,
Those default settings are suited for sealed batteries, not flooded. While
each battery manufacturer's charge protocols are somewhat different, I
would definitely follow Trojan's recommendations as best possible in this
circumstance.
Howie
Howie Michaelson
NABCEP Certified Solar PV Installer™
Sun Catcher
Renewable Energy Systems Sales and Service
VT Solar Electric Incentive Partner
802-272-0004
On Jan 18, 2016 11:33 PM, "William Miller" <william at millersolar.com> wrote:
> Colleagues:
>
>
>
> I have an off-grid customer for whom I replaced a set of 8 Trojan L-16s as
> well as upgrading her inverter and charge controller. Right after the job,
> we found several batteries with low specific gravity. We spoke with the
> local distributor and received two replacement batteries.
>
>
>
> The system continues to perform poorly. The customer EQs every 30 days to
> 60 plus volts for 3 hours. They try to get a full bulk and absorption
> charge in every day but this time of year may not. The specific gravity
> readings continue to diverge and generally go lower.
>
>
>
> We contacted the distributor who told us they have had problems with
> Trojan batteries since the company was sold about two years ago. We were
> told they had a brand X battery that tested better than the Trojans. We
> agreed to try the Brand X but then were told that we had not charged the
> Trojans adequately. Below are the settings recommended directly by Trojan
>
>
>
> These settings are significantly higher than any I have used before.
> Also, I don’t recall it being possible to set different bulk and absorption
> voltages with any of the equipment I use. I use Trace, Outback, Schneider
> default settings of 57.6 bulk, 54.4 float and reprogram to 60.5 for
> equalization.
>
>
>
> I am curious about what charge settings you find successful for flooded
> lead-acid batteries and what any of you might think about the recommended
> settings as seen below. Do you feel it is practical to achieve these
> settings in an off-grid scenario? Would these high settings cause
> excessive water consumption?
>
>
>
> Thanks in advance.
>
>
>
> William Miller
>
>
>
> [image: Gradient Cap_mini]
> Lic 773985
> millersolar.com <http://www.millersolar.com/>
> 805-438-5600
>
>
>
>
>
>
>
> I looked at the spreadsheet and the SG. readings across each battery are
> uniform which tells be that it is highly unlikely that anything is wrong
> with the batteries except for being under-charged. Take a look at our
> User’s Guide on the Trojan website on page 19 ( Recommended Charge
> Profile) or FLA batteries.
>
> The Bulk stage should be @ 59.3V, Absorb @ 58.8V, Float @ 54V and
> Equalization @ 64.8V. When the User notices drops in the SG such as in this
> document, an EQ charge should be performed in order to get the batteries
> back up to full charge (full charge SG being in the range of 1.270 to
> 1.280. When performing the EQ, the user should take SG reading for a
> “pilot” battery every 30 minutes until the voltages reach that range.
> Termination should happen when SG reaches full charge range or if battery
> temperature reaches 112 degrees F, which-ever comes first. SG readings can
> be taken during EQ, but you have to make sure that you bump the tiny gas
> bubbles off the Hydrometer float to prevent erroneous readings.
>
> Seeing the SG readings decreasing after each month is an indication that
> maybe the Absorb Time needs to be increased, maybe from 3 hours up to 4 or
> 5 hours.
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160118/c6f5941e/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1460 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160118/c6f5941e/attachment-0004.jpg>
More information about the RE-wrenches
mailing list