I recently assessed a 22 year old Trace 4024. During bulk charge mode, I
noticed that the charge would go from about 18A down to 5-6A every 15-20
seconds, and then repeat the cycle. I observed this for about 5 minutes
relatively consistently I also noticed the body of the 4024 was very hot,
and I couldn't feel a fan moving air through it.
I put a fan on it and blew air over the body of the inverter, trying to
direct it through the machine. While I did that, I never observed it drop
out again over about 5 minutes, so I'm assuming that there is an internal
cooling fan that has gone out.
It's been quite a while since I opened one of these up. Does anyone know
what's involved in replacing a cooling fan on one of these? Is it worth it
on a 22 year old inverter?
Thanks in advance
--
Mac Lewis