[RE-wrenches] Generator factory wiring issues

Kevin Pegg KPegg at energyalternatives.ca
Tue May 24 15:14:07 PDT 2016


Wrenches,

Recently, we took delivery of a 40 kW LPG generator made by Gillette.

Inspecting the factory wiring of the unit, I had some concerns which are outlined in detail below, with an engineer's response inline. The concerns are using #4 wire to pull 175A; no plastic bushings on metallic conduit, and ground lugs on top of painted surfaces / and insufficiently torqued.

The engineer response has left me somewhat baffled / frustrated in that I do not feel that actual issues have been addressed. I don't really care what UL or any other authority tells me - pulling 175A continually for many hrs through a #4 wire I think is asking for trouble. And my customer won't really care about what the UL ratings say if they are dealing with a melted alternator.

Am I missing something here?

Kevin


RE: SP-410-1-1LO     S/N:

I am responding to the concerns written below both in the capacity as designer and as U.L. liaison.

We have received this generator, mostly intact. Some freight damage to the battery support cross member due to forks not extending the full depth of the crate, and are working with the freight company to resolve that.
Sorry for the experienced freight damage.

However, there are some SERIOUS and DANGEROUS issues pertaining to the wiring of the alternator! It is obvious that wiring was not done by an electrician.
There are no serious or dangerous issues on this (built to U.L. recognized spec) Gillette Generator as referred to in this writing. And - you are correct- this wiring, as 'factory wiring and not 'field' wiring, does not require or use the specific qualifications of a licensed electrician. The well trained/supervised workers here at Gillette have many years of experience building the product and are guided as need by a competent engineering staff.

Specifically:

- Alternator to circuit breaker wiring was done with #4 wire (rated 60A max). Per your own load chart inside the breaker enclosure (photo attached), that wire should be 4/0 to carry the 175A that this generator is capable of producing.
This observation is incorrect. The load wiring sizing schedule affixed to the side of the circuit breaker box is for 'field connectivity' at 75 deg. F. We do our 'factory wiring ' on a different schedule using load cabling from the generator to the top of the circuit breaker rated at 150 deg. F. All of this cabling has been done, tested and proven by U.L

- There were no plastic bushings (see photo) where the wires exit the metal conduit.
The conduit bushing involved is the correct U.L. approved component for the installation of spiral wound metal conduit required to be installed on 'open' style generator assemblies. A plastic bushing is NOT required as this is again 'factory wiring', not 'field wiring.

- What would have happened here is the wire heats up due to gross under sizing, melts the insulation, and shorts it out. Resulting in a fire or destruction of the brand new alternator, and the associated legal proceedings involving all parties and a general nightmare for all of us.
 disagree, on several fronts. Referencing the specification standard U.L. 2200, many times- local inspectors blur the line between its dominance for standby generator systems and NEC-70 (NEC- code). The former covers 'factory' design wiring on stationary standby generators subject to witness testing by a U.L. certified representative. The latter applies to 'field wiring'- that is anything outside the box including connection conduits, load wiring ( at 75 deg. F) transfer switches, distribution panes and the like. As resident designer for the past twenty-six years, I have myself- written eight standards/code rebuttals successfully, both for U.L. and local inspectors. Comparing a 4ga, 2ga, 1ga and the like against a different class of wiring such as a 4/0 would certainly be cause for alarm. But, clearly here the alarm is unwarranted.

                - the ground lug on the alternator was not fastened properly (a short stud with a nut on it - no way to get proper torque on it - should be a bolt), and both this lug and the lug inside the breaker enclosure was fitted on top of a painted surface. Every electrician knows you need to scrape off the paint so as to allow for proper conductivity.
This lug is not supplied by us. It is supplied as part of the generator construction built by Marathon. Marathon generators are certified for U.L. 1004B- generator assemblies and U.L. 1446 for insulation. This is the equipment issued as part of that U.L. certified design. as to their design vs. a 'bolt' going into the threads of the hole-  if it was really an issue, it would not have passed their U.L. certification testing. Their generator assemblies bear their U.L. file certification under R/C (JZGZ2) and listing (JZGZ). In regards to the paint removal, the engine and generator are cable grounded to the frame of the generator assembly and serrated hardware is used during assembly to scratch into the painted surfaces of the boxes and frame. As you notice in the picture- the threads in the generator housing sleeve- are not painted.

                These are issues that we are able to remedy. But my client, being very hands on has noticed this and inquired, quite reasonably, as to why they are paying Energy Alternatives to repair something that they paid for and should have been delivered properly done in the first place?
To my findings, there is no warrantable work required.

                I think the fairest solution to this is for us to remedy these defects and to have Collicutt reimburse use for time and materials. I will complete the work and send you the total bill for compensation unless you would like to approach this in a different method. We are hoping to go live with this unit in the next few days once the gas fitting is completed.
As stated above- Not required.

I hope these responses help clarify the items in question.


Regards,