Kris,
I'm just looking into re-stocking some cable ties and came across this
thread when searching my email for cable tie/management part numbers...
The photos you shared remind me of a system i saw recently that was
installed by a competitor here (and who happens to teach a PV install
training course).  The system i saw is similar in that there are many PV
wires clearly visible, unprotected and laying on the roof and these are a
perfect example of inspectors not doing their job properly.

I get it that "liability" keeps electrical inspectors from climbing ladders
onto the roof to inspect the array install up close, but when poor wire
management like these examples can clearly be seen from the ground and the
inspectors are not noting the wire management (or lack of) as a
deficiency.... they are either not properly trained in what to look for and
have no place inspecting PV systems or are simply not doing their job
properly and have no place inspecting anything.

*Benn Kilburn *
CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Energy Inc
6706 – 82 Ave NW | Edmonton, AB | T6B 0E7
P: 780-474-8992 | F: 888-405-5843 | www.skyfireenergy.com
[image: email] <benn at skyfireenergy.com> [image: facebook]
<https://www.facebook.com/SkyFireEnergy> [image: twitter]
<https://twitter.com/SkyFireEnergy> [image: linkedin]
<https://www.linkedin.com/company/283735?trk=tyah&trkInfo=tarId%3A1408655033432%2Ctas%3Askyfire%2Cidx%3A2-2-5>
 [image: google] <https://plus.google.com/+SkyFireEnergy/>

[image: SkyFire Energy Logo_horizontal]

On Fri, Dec 11, 2015 at 9:01 AM, Kristopher Schmid <solman at legacysolar.com>
wrote:

> I just have to post an example of how to do it wrong (courtesy of one of
> my competitors).  Pictures attached.  This passed an inspection...
>
> On Wed, Dec 9, 2015 at 8:06 AM, Rebekah Hren <rebekah.hren at gmail.com>
> wrote:
>
>> Hi,
>> Wondering if anyone has insight into Code requirements for
>> securing/supporting PV wire behind the modules?
>>
>> I am aware that USE-2 sends you to Section 334.30 requirements for Type
>> NM (12" from box, every 4.5 ').
>>
>> However, I think this is totally bogus, for 2 reasons.
>> 1) Section 338.10(B)(4)(b) that refers the NM article is titled "Branch
>> circuits or Feeders."  These are PV source and output circuits, not branch
>> circuits or feeders.
>>
>> 2) it is nearly IMPOSSIBLE to secure the PV wire within 12" of the module
>> junction box for many modules, especially in landscape wiring, without
>> causing more harm than good, too tight a bending radius, stress on
>> conductors.
>>
>> 334.40(B) maybe leaves a little wiggle room for concealed spaces in
>> structures where it is impracticable to support.
>>
>> My big problem here is that both requirements of 334.30 are useless or
>> harmful to PV systems. 12" to the box is often impossible, and 4.5" feet is
>> too long to go without any support behind the array!!! I just noticed there
>> was a proposal in 2017 to Codify the 334.40 requirements for PV cables and
>> so I guess I only have myself to blame for not writing a better proposal at
>> this point.
>>
>> Rebekah
>> --
>> Tel: 336.266.8800
>> NABCEP Certified Solar PV Installation Professional™ 091209-85
>> NC Licensed Electrical Contractor
>>
>>
>>
>>
>
>
> --
> Shine On!
>
> Kris Schmid
> Legacy Solar, LLC
> 864 Clam Falls Trail
> Frederic, WI 54837
> www.legacysolar.com
> 715-653-4295
> NABCEP Certified PV Installer
> Licensed Wisconsin Master Electrician
> BSEE
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160207/fc2b6d19/attachment-0002.html>


More information about the RE-wrenches mailing list