[RE-wrenches] SMA Arc-Fault

frank -bz products bzp at brick.net
Thu Nov 10 13:32:29 PST 2016


I have found that single point grounding in large complex systems can 
solve a lot strange problems. Just a thought.


BZ Products INC.
8801 Gravois Rd.
St.Louis MO 63123 USA
314-644-2490
www.bz-products.net

On 11/10/2016 3:20 PM, Drake wrote:
> Is your array on a large metal roof, or is it where intense radio 
> signals could be getting picked up by your racking? Either of these 
> conditions could potentially be your problem.
>
> At 01:37 PM 11/10/2016, you wrote:
>> Daryl,Â
>> That is what I thought at first. Very rare, but I suppose not 
>> impossible that IÂ
>> would have two inverters with bad arc fault detectors. But since we 
>> are still
>> getting arc faults after replacing the inverters, I am thinking that 
>> it must be
>> something else.
>>
>> Cheers,Â
>> Dave
>>
>>
>> *--
>>
>> Dave Tedeyan**
>> Project Engineer
>> *
>> *Taitem Engineering, PC
>> *109Â S. Albany Street, Ithaca, NY 14850
>> Voice:Â (607) 277-1118 x121 <??>
>> www.taitem.com <http://www.taitem.com/>
>>
>> On Thu, Nov 10, 2016 at 1:18 PM, <penobscotsolar at midmaine.com 
>> <mailto:penobscotsolar at midmaine.com>> wrote:
>>
>>     There is at least one company (nameless at this point, but not
>>     SMA) that
>>     has been providing replacements for swapping out faulty arc fault
>>     detectors in their inverters. Could it be possible you have a bad
>>     detector?
>>
>>     Daryl
>>
>>
>>
>>     > Hi All,
>>     >
>>     > Maybe someone will have some ideas for why a couple inverters
>>     keep arc
>>     > faulting:
>>     >
>>     > -There are two SB7000TL-22 inverters, Sunpower branded.
>>     > -3 Strings of 7 SPR-327's to each inverter. Kept separate until the
>>     > inverter.
>>     > -Ground mount about 50' from the shed where the inverters are
>>     located
>>     > (indoors)
>>     > -Simple grid connected system, no batteries.
>>     > -There is a whole house generator co-located in the shed.
>>     > -We interconnect by using piercing taps on the line side of the
>>     generator
>>     > transfer switch
>>     > -There has been only one power outage there since the system
>>     was installed
>>     > in April, but the generator fires up weekly.
>>     >
>>     > -The arc faults have been happening on both inverters.
>>     Sometimes only one
>>     > at a time, sometimes both will go within a day of each other.
>>     > -The events have been approximately one a month, but sometimes
>>     more,
>>     > sometimes less.
>>     >
>>     > -We have already checked every single connection in the system
>>     twice, by
>>     > two different people.
>>     > -We have replaced the underground wires (and they looked just fine)
>>     > -We have replaced all home runs.
>>     > -We have replaced both inverters.
>>     > -Arc faults are still happening.
>>     > -Arc faults are not always on the same day/time of the week.
>>     >
>>     > I am wondering if this can be caused by the generator?
>>     > Has anyone run into a situation like this or something similar?
>>     >
>>     > Thanks for your help,
>>     > Dave
>>     >
>>     > *--*
>>     >
>>     >
>>     > *Dave Tedeyan*
>>     > *Project Engineer*
>>     >
>>     > *Taitem Engineering, PC*
>>     > 109 S. Albany Street, Ithaca, NY 14850
>>     > Voice: (607) 277-1118 x121 <tel:%28607%29%20277-1118%20x121>
>>     > www.taitem.com <http://www.taitem.com>
>>     > _______________________________________________
>>     > List sponsored by Redwood Alliance
>>     >
>>     > List Address: RE-wrenches at lists.re-wrenches.org
>>     <mailto:RE-wrenches at lists.re-wrenches.org>
>>     >
>>     > Change listserver email address & settings:
>>     >
>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>     >
>>     > List-Archive:
>>     >
>>     http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>>     >
>>     > List rules & etiquette:
>>     > www.re-wrenches.org/etiquette.htm
>>     <http://www.re-wrenches.org/etiquette.htm>
>>     >
>>     > Check out or update participant bios:
>>     > www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>     >
>>     >
>>
>>
>>     _______________________________________________
>>     List sponsored by Redwood Alliance
>>
>>     List Address: RE-wrenches at lists.re-wrenches.org
>>     <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>>     Change listserver email address & settings:
>>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>     List-Archive:
>>     http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>>
>>     List rules & etiquette:
>>     www.re-wrenches.org/etiquette.htm
>>     <http://www.re-wrenches.org/etiquette.htm>
>>
>>     Check out or update participant bios:
>>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
>>
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm 
>> <http://www.re-wrenches.org/etiquette.htm>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>
>
> ------------------------------------------------------------------------
> Avast logo 
> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient> 
> 	
>
> This email has been checked for viruses by Avast antivirus software.
> www.avast.com 
> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient> 
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20161110/ffc4ca4e/attachment.html>


More information about the RE-wrenches mailing list