[RE-wrenches] PV Recombiner
William Miller
william at millersolar.com
Mon Oct 10 21:52:41 PDT 2016
Jason:
I thought of this but I can find no DIN rail mounted breakers that perform
a GFDI function and are rated for 60 or 80 amps continuous. Do you know
of any? Midnite has a 63 amp unit, but this won’t work for FM80
controllers, and if it is not rated for continuous duty, it won’t work for
an FM60 either.
We have used an Outback Flexware 1000 DC Cabinets for recombiners. They
have the same issue with back wiring but there is more room
William
PS: I was on the island a couple of weeks ago. Sorry I did not run into
you.
Wm
[image: Gradient Cap_mini]
Lic 773985
millersolar.com <http://www.millersolar.com/>
805-438-5600
*From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
Behalf Of *Jason Lerner
*Sent:* Monday, October 10, 2016 8:26 PM
*To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
*Subject:* Re: [RE-wrenches] PV Recombiner
Hello William,
How about using an Outback Flexware 500/1000 AC circuit breaker box with DC
rated DIN rail mounted breakers? The Main breaker might need to live in
the GSLC though…..
Best,
Jason Lerner
Waldron Power and Light Co.
On Oct 10, 2016, at 2:55 PM, William Miller <william at millersolar.com> wrote:
Friends:
I am looking for a PV recombiner. I need to accept the outputs from 3
remote PV Combiners, send those outputs through GFP circuit breakers, into
charge controllers, back thorough breaker, into a bus bar, through a main
breaker and onto a large battery bank.
I am using 2 Outback Radian inverters, but I refuse to install DC breakers
on their dead-front because wiring to studs facing away from the front is
an inferior design. Furthermore, I see no need to run PV circuits through
the GSLC cabinets.
I looked at the Midnite MNDC15 but again, these use panel mounted breakers
with studs on the back.
Anyone know of a more thoughtfully designed PV recombiner?
Thanks in advance,
William Miller
<image003.jpg>
Lic 773985
millersolar.com <http://www.millersolar.com/>
805-438-5600
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20161010/7b9f643e/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1460 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20161010/7b9f643e/attachment-0002.jpg>
More information about the RE-wrenches
mailing list