Wire them to the utility side of the transfer switch, Auto restart and probably manufacture recommended method of connection when used in conjunction w/ gen set. T
> On Sep 8, 2016, at 1:00 PM, Benn Kilburn <benn at skyfireenergy.com> wrote:
> 
> Wrenches,
> We are installing 2 SolarEdge SE7600A-US inverters in a grid-tied system that has a 15kw back-up generator on an auto transfer switch.
> 
> The generator is located in a shed about 300' or more away and the feeders to the house are underground.
> Inverters are located in the house basement mechanial room along with the house electrical panelboard.
> 
> We are looking for relay options to shut down the inverters when there is a power interruption, before the generator kicks in.  This could be a manual reset.
> 
> What are some options you have seen/used for something like this?
> 
> Thanks,
> 
> Benn Kilburn 
> CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Energy Inc
> 14515 – 121A Ave NW | Edmonton, AB | T5L 2T2
> P: 780-474-8992 | F: 888-405-5843 | www.skyfireenergy.com <http://www.skyfireenergy.com/> <mailto:benn at skyfireenergy.com>  <https://www.facebook.com/SkyFireEnergy>  <https://twitter.com/SkyFireEnergy>  <https://www.linkedin.com/company/283735?trk=tyah&trkInfo=tarId%3A1408655033432%2Ctas%3Askyfire%2Cidx%3A2-2-5>
> 
> 
> WE HAVE MOVED! Please note our new address above.
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 

> Tump at swnl.net <blocked::mailto:Tump at swnl.net%22%20%5Co%20%22blocked::mailto:Tump at swnl.net>               www.SWNL.net <blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
>                 Solarwinds Northernlights       
>        Serving Mid Coast Maine & Northern California
>                          207-832-7574   Cl. 610-517-8401                              
>                               Blair "TUMP" May
>                ********  MAINE'S CHARTER ********
>                       NABCEP    "Certified PV Installer" 
>    
>               ********  MAINE'S CHARTER ********
>                   Trace Xantrex "Certified" Dealer / Installer"
> 


-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160909/b8ce247d/attachment-0001.html>


More information about the RE-wrenches mailing list