[RE-wrenches] Interconnection for multi-meter setups

Jerry Shafer jerrysgarage01 at gmail.com
Tue Jun 14 20:42:29 PDT 2016


Wrenches
We do allot of these ourselves and, it seems each is different but the last
one was 18 units plus the common all got load side taps with fused 30 amp
discos, we have also had line side but your panel is hard bused and a load
side is the only way. There is a new breaker out but last I heard it is not
UL approved I have left them messages with no response. Our utility
requires disco's so it works out OK this way. the paperwork is crazy for
this with all the little systems.
Jerry

On Tue, Jun 14, 2016 at 12:57 PM, August Goers <august at luminalt.com> wrote:

> Hi Wrenches,
>
>
>
> We’re installing on a lot of multifamily buildings these days. Does anyone
> have a clue how to apply NEC 705.12 interconnection rules to the type of
> setup in the attached photo? In this case, we have a 200 A or 400 A main
> service disconnect feeding a 9-meter bank. The meter bank appears to be
> setup so that each meter is fed from the main disconnect by factory
> bussing. Each individual meter has a 70 A breaker feeding a remote sub
> panel. We want to install a 50 A solar breaker. We can interconnect at one
> of the existing meters or possibly install a new solar-service in one of
> the blank meter spots.
>
>
>
> Cheers,
>
>
>
> August
>
>
>
> Luminalt
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160614/fd8430d6/attachment-0001.html>


More information about the RE-wrenches mailing list