UL evaluates products on internal temperature rises while it is used 
normally.

They also evaluate the products under abnormal use, in various ways.

It may or may not have a fan.  If you look inside an inverter, you will 
see the same type of

things....  Large external battery cables connecting to smaller internal 
cables and/or

bus-bars and circuit board traces.  All sorts of things that probably 
are not allowed

with NEC.


I think I  saw a temperature of 150 degrees F mentioned here. That's nothing

compared to the highest temperatures seen in certain parts of the products.

Some wire, like in some transformer classes can reach as high as 220 
degrees C (428 F) !


boB



On 5/25/2016 11:39 AM, Kevin Pegg wrote:
>
> Hi Daniel,
>
> Appreciate your thoughts on this.
>
> - This wire is contained inside 2" flexible metallic conduit, approx. 
> 3' long from the alternator to the external breaker. Some of it is in 
> free air, but most is contained within the conduit.
>
> - the main breaker is a 100% rated 175A.
>
> - This is an industrial generator is rated for continual operation at 
> full load, and my expectations is all the wiring in that unit is 
> suited to that. Will the site actually draw that? It is entirely 
> possible during heavy loads & concurrent battery charging that it 
> could well be running at max load for hrs at a time.
>
> The plastic bushing is easy to remedy, as is the ground lug.
>
> The wire is where I am not sure what to do. Everything I am hearing 
> tells me that the #4 wire is undersized. So there is a dilemma. If I 
> replace the wires myself then I believe I have voided the UL 
> certification. But think have made a safer engine for my client. At 
> the end of the day, it will be me who the client is calling if there 
> is an issue.
>
> Just for kicks I opened up a couple 25 kW gens and factory wiring was 
> either # 2 or # 4 for this same purpose. Hmm.
>
> Kevin
>
> *From:*RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] 
> *On Behalf Of *Daniel Young
> *Sent:* May-25-16 7:24 AM
> *To:* 'RE-wrenches' <re-wrenches at lists.re-wrenches.org>
> *Subject:* Re: [RE-wrenches] Generator factory wiring issues
>
> Kevin,
>
> Based on what the engineer said, I think you both make valid points.
>
> On the 4AWG wire:
>
> Type Z wire (150 C insulation) is rated for 190A based on 2014NEC 
> table 310.15(B)(19). It’s rated for 120A when in conduit. So is this 
> wire where you might call it in conduit or free air? I imagine the 
> inside of a generator enclosure is somewhere in the middle. Also I 
> assume this is Z type or similar based on the response stating 150 F 
> (I know he meant C) wiring is used.
>
> Is this on a 175A breaker? If so then it should only pull 140A 
> continuous (maybe it’s a 100% rated breaker?). And that really would 
> not be great for a generator. Usually we only design for a maximum of 
> 80% loading on a generator depending on elevation and a few other 
> de-rate factors. In reality do you expect more than 120A to be a true 
> “continuous” load on this unit. I don’t know the answer, just worth 
> thinking about.
>
> Plastic bushings:
>
> I sure would want them in a vibrating machine like a generator, but if 
> UL does not force them to, don’t expect them to include it. 
> (Capitalism at work). You might be able to use an electricians trick 
> where you cut a PVC bushing and slip it over the existing wire, then 
> you can thread it in the end of the fitting and it is 95% as good as a 
> normally installed bushing…. I would not do it on a new install, but 
> it’s a useful trick when you walk up on existing mistakes.
>
> Lug:
>
> You could continuity test it to see if it’s a good connection, 
> otherwise that strikes me as no good either. Just another cost saving 
> step for the manu at the clients expense in my opinion. It’ll work 
> fine for now, but not likely in 5-10yrs as corrosion sets in. I’d just 
> throw a star washer underneath if possible, but it sounds like the 
> stud is not long enough.
>
> So there is a little bitta’ code and a lotta’ opinion.
>
> With Regards,
>
> Daniel Young,
>
> NABCEP Certified PV Installation Professional^TM : Cert #031508-90
>
> *From:*RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] 
> *On Behalf Of *Kevin Pegg
> *Sent:* Tuesday, May 24, 2016 6:14 PM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org 
> <mailto:re-wrenches at lists.re-wrenches.org>>
> *Subject:* [RE-wrenches] Generator factory wiring issues
>
> Wrenches,
>
> Recently, we took delivery of a 40 kW LPG generator made by Gillette.
>
> Inspecting the factory wiring of the unit, I had some concerns which 
> are outlined in detail below, with an engineer's response inline. The 
> concerns are using #4 wire to pull 175A; no plastic bushings on 
> metallic conduit, and ground lugs on top of painted surfaces / and 
> insufficiently torqued.
>
> The engineer response has left me somewhat baffled / frustrated in 
> that I do not feel that actual issues have been addressed. I don't 
> really care what UL or any other authority tells me - pulling 175A 
> continually for many hrs through a #4 wire I think is asking for 
> trouble. And my customer won't really care about what the UL ratings 
> say if they are dealing with a melted alternator.
>
> Am I missing something here?
>
> Kevin
>
> RE: SP-410-1-1LO     S/N:
>
> I am responding to the concerns written below both in the capacity as 
> designer and as U.L. liaison.
>
> We have received this generator, mostly intact. Some freight damage to 
> the battery support cross member due to forks not extending the full 
> depth of the crate, and are working with the freight company to 
> resolve that.
>
> Sorry for the experienced freight damage.
>
> However, there are some SERIOUS and DANGEROUS issues pertaining to the 
> wiring of the alternator! It is obvious that wiring was not done by an 
> electrician.
>
> There are no serious or dangerous issues on this (built to U.L. 
> recognized spec) Gillette Generator as referred to in this writing. 
> And – you are correct- this wiring, as ‘factory wiring and not ‘field’ 
> wiring, does not require or use the specific qualifications of a 
> licensed electrician. The well trained/supervised workers here at 
> Gillette have many years of experience building the product and are 
> guided as need by a competent engineering staff.
>
> Specifically:
>
> - Alternator to circuit breaker wiring was done with #4 wire (rated 
> 60A max). Per your own load chart inside the breaker enclosure (photo 
> attached), that wire should be 4/0 to carry the 175A that this 
> generator is capable of producing.
>
> This observation is incorrect. The load wiring sizing schedule affixed 
> to the side of the circuit breaker box is for ‘field connectivity’ at 
> 75 deg. F. We do our ‘factory wiring ‘ on a different schedule using 
> load cabling from the generator to the top of the circuit breaker 
> rated at 150 deg. F. All of this cabling has been done, tested and 
> proven by U.L
>
> - There were no plastic bushings (see photo) where the wires exit the 
> metal conduit.
>
> The conduit bushing involved is the correct U.L. approved component 
> for the installation of spiral wound metal conduit required to be 
> installed on ‘open’ style generator assemblies. A plastic bushing is 
> NOT required as this is again ‘factory wiring’, not ‘field wiring.
>
> - What would have happened here is the wire heats up due to gross 
> under sizing, melts the insulation, and shorts it out. Resulting in a 
> fire or destruction of the brand new alternator, and the associated 
> legal proceedings involving all parties and a general nightmare for 
> all of us.
>
>  disagree, on several fronts. Referencing the specification standard 
> U.L. 2200, many times- local inspectors blur the line between its 
> dominance for standby generator systems and NEC-70 (NEC- code). The 
> former covers ‘factory’ design wiring on stationary standby generators 
> subject to witness testing by a U.L. certified representative. The 
> latter applies to ‘field wiring’- that is anything outside the box 
> including connection conduits, load wiring ( at 75 deg. F) transfer 
> switches, distribution panes and the like. As resident designer for 
> the past twenty-six years, I have myself- written eight standards/code 
> rebuttals successfully, both for U.L. and local inspectors. Comparing 
> a 4ga, 2ga, 1ga and the like against a different class of wiring such 
> as a 4/0 would certainly be cause for alarm. But, clearly here_the 
> alarm is unwarranted_.
>
>                 - the ground lug on the alternator was not fastened 
> properly (a short stud with a nut on it - no way to get proper torque 
> on it - should be a bolt), and both this lug and the lug inside the 
> breaker enclosure was fitted on top of a painted surface. Every 
> electrician knows you need to scrape off the paint so as to allow for 
> proper conductivity.
>
> This lug is not supplied by us. It is supplied as part of the 
> generator construction built by Marathon. Marathon generators are 
> certified for U.L. 1004B- generator assemblies and U.L. 1446 for 
> insulation. This is the equipment issued as part of that U.L. 
> certified design. as to their design vs. a ‘bolt’ going into the 
> threads of the hole-  if it was really an issue, it would not have 
> passed their U.L. certification testing. Their generator assemblies 
> bear their U.L. file certification under R/C (JZGZ2) and listing 
> (JZGZ). In regards to the paint removal, the engine and generator are 
> cable grounded to the frame of the generator assembly and serrated 
> hardware is used during assembly to scratch into the painted surfaces 
> of the boxes and frame. As you notice in the picture- the threads in 
> the generator housing sleeve- are not painted.
>
>                 These are issues that we are able to remedy. But my 
> client, being very hands on has noticed this and inquired, quite 
> reasonably, as to why they are paying Energy Alternatives to repair 
> something that they paid for and should have been delivered properly 
> done in the first place?
>
> To my findings, there is no warrantable work required.
>
>                 I think the fairest solution to this is for us to 
> remedy these defects and to have Collicutt reimburse use for time and 
> materials. I will complete the work and send you the total bill for 
> compensation unless you would like to approach this in a different 
> method. We are hoping to go live with this unit in the next few days 
> once the gas fitting is completed.
>
> As stated above- Not required.
>
> I hope these responses help clarify the items in question.
>
> Regards,
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160525/23badf63/attachment.html>


More information about the RE-wrenches mailing list