[RE-wrenches] Goofy roofing
frenergy
frenergy at psln.com
Sat Apr 30 07:47:03 PDT 2016
Benn, August, etc
Sorry for omitting a somewhat crucial detail....below these
stringers it is a "standard" residential stacked roof with 2X6 rafters
on 16" centers with 1/2 " plywood deck. No purlins. I appreciate the
feedback/good ideas.
Bill
Feather River Solar Electric
On 4/29/2016 3:28 PM, August Goers wrote:
>
> Benn,
>
> We’ve done it several ways including putting four 14 x 1.5” TYPE 17
> screws per attachment point through the metal and into the 1” x wood
> purlin. The key is that the load path all the way down needs to be
> capable of handling the worst case loads. So we had to check that too.
> Some racking manufactures such as Unirac have online calculators to
> give point loads.
>
> Best, August
>
> *From:*RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org
> <mailto:re-wrenches-bounces at lists.re-wrenches.org>] *On Behalf Of
> *Benn Kilburn
> *Sent:* Friday, April 29, 2016 2:17 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Goofy roofing
>
> August, et al;
>
> If the purlins are only 1"x4" or 1"x6" or....1"x anything, are you
> only relying on the 1" purlin as the attachment point or are you
> hitting the vertical trusses below the purlins?
>
> We are working on a corrugated roof right now and using a Schletter
> roof bracket. The name of it escapes me at the moment. Maybe FixT?
>
> We are attaching to purlins which are 2"x6". I wouldn't think 1"x
> anything would provide enough pull-out?
>
> Benn Kilburn
>
> SkyFire Energy Inc.
>
> 780-906-7807
>
>
> On Apr 29, 2016, at 9:09 AM, August Goers <august at luminalt.com
> <mailto:august at luminalt.com>> wrote:
>
> Hi Bill,
>
> It sounds like you’re talking about a purlin type setup – 4’
> sounds a little far apart but I guess that’s what you have to deal
> with. If you have a corrugated metal roof, we’ve used S-5
> CurruBrackets screwed through the metal and into the purlins and
> then either run the solar rail up and down the roof or install a
> sub-rack system (with strut or angle aluminum) perpendicular to
> your solar rail.
>
> Best,
>
> August
>
> *From:*RE-wrenches
> [mailto:re-wrenches-bounces at lists.re-wrenches.org
> <mailto:re-wrenches-bounces at lists.re-wrenches.org>] *On Behalf Of
> *frenergy
> *Sent:* Friday, April 29, 2016 6:55 AM
> *To:* RE-wrenches
> *Subject:* [RE-wrenches] Goofy roofing
>
> Recently, a customer had a metal roof (not standing seam)
> installed by a "handyman". Pretty clean installation however for
> some reason he ran 1X6 stringers across the roof on the 1/2"
> plywood deck spaced about every 4 feet (as you go from ridge to
> eaves). Of course the roofing screws are at the stringers. I'm
> sure he had a /great/ reason for doing so. So now I have been
> asked to install an array on this roof. You can feel how "soft"
> the roof is as you walk on it of course because you are walking on
> air-below-metal for most of the roof. Stringer locations don't
> jive with possible feet/post locations for rail. I'm usually
> pretty good at problem solving but I'm accepting ideas.
>
> Bill
>
> Feather River Solar Electric
>
> Bill Battagin, Owner
>
> 4291 Nelson St.
>
> Taylorsville, CA 95983
>
> 530.284.7849
>
> CA Lic 874049
>
> www.frenergy.net <http://www.frenergy.net>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
> <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
--
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049
www.frenergy.net
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160430/23843ead/attachment.html>
More information about the RE-wrenches
mailing list