[RE-wrenches] SolarEdge comm card failures

Howie Michaelson howie at suncatchervt.com
Mon Apr 18 11:26:42 PDT 2016


Carl,

We experienced a rash of Comm Card issues with several SE installs over
several years, but none exactly as you describe.  Our issues were almost
all resolved with a board replacement, but a few were particularly vexing
with many return service calls to get a resolution.  We seemed to have the
most problems with the single phase 10k inverters.  In general, SE tech
support was helpful, although a bit paint-by-numbers at times, as well as
very slow to answer for much of 2015.  As best I can tell, the issues have
begun to settle down most recently.
Howie

*Howie Michaelson*
*NABCEP Certified Solar PV Installer™*
Sun Catcher, LLC
Renewable Energy Systems Sales and Service
VT Solar Electric Incentive Partner
802-272-0004

On Mon, Apr 18, 2016 at 11:34 AM, Carl Adams <swingjunkie at gmail.com> wrote:

> Hello Wrenches,
>
> Anyone experiencing issues with comm card failures on SolarEdge
> inverters?  We have some systems installed  in 2012 exhibiting similar
> behaviors.  The systems are producing data, it is registering on the
> inverter, and our independent utilty meter, but is not reported to the
> SolarEdge portal.  Next day(s) it reports production to the portal but the
> missing data is never filled in.  I have attached a small graph from the
> portal dashboard.
>
> Typically if a network connection goes down, and then is restored the data
> should be uploaded after the connection is back on line.  In this case
> their remains a hole in the data, for that day, indicating that data was
> never uploaded.
>
> We had one system which exhibited this "missing data" symptom on accasion
> over a 2 month period of time.  This was diagnosed, as a failing comm
> card.  Once that was replaced we have not seen the issue recur for that
> site.  But now we are seeing similar behavior from three other sites, all
> installed a in the second half of 2012.
>
> Just wondering if anyone else has encountered this.
>
> Thanks
> Carl Adams
> SunRock Solar
>
>
> <https://www.avast.com/en-us/lp-safe-emailing-2109?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=oa-2109-v2-a> Virus-free.
> www.avast.com
> <https://www.avast.com/en-us/lp-safe-emailing-2109?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=oa-2109-v2-a>
> <#m_3325038974001079228_DDB4FAA8-2DD7-40BB-A1B8-4E2AA1F9FDF2>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160418/3f2413e4/attachment.html>


More information about the RE-wrenches mailing list