[RE-wrenches] Specific AC Coupling question
Ray Walters
ray at solarray.com
Mon Apr 4 21:06:27 PDT 2016
Also worth looking at Magnum's new AC diversion load system. It does
the frequency shifting but also 4 kw dump load that can be set up to any
AC electric load.
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 4/4/2016 6:45 PM, jay wrote:
> HI Allan,
>
> The only reason to frequency shift is for “softer” charging.
> VRLA are not as sensitive to the pulse type charging that a relay type
> charging would do.
> And regardless if you have frequency shift or not, you will still need
> ( especially with VRLA) a high voltage relay.
> I recommend a SS relay, but a regular mechanical contactor will do as
> well.
>
> jay
>
> Peltz Power.
>
>
>
>> On Apr 4, 2016, at 12:34 PM, Allan Sindelar <allan at sindelarsolar.com
>> <mailto:allan at sindelarsolar.com>> wrote:
>>
>> Wrenches,
>> Core question first: Will a ~2010 Fronius IG-4000 respond properly to
>> the frequency shift regulation supplied by a new Schneider XW+5548 or
>> XW+6848?
>>
>> Situation: I haven't seen the Colorado site; I'm working as a
>> consultant to produce an upgrade component list and will later serve
>> as a resource during local installation of the upgrade equipment.
>> Customer has hired me to turn a hodgepodge system into a GTBB system.
>> The system has two key parts: an existing SW5548 with batteries,
>> never properly installed (only AC1 in was ever connected to a main
>> load center!) with 3.1 kW of tracker-mounted PV through an Outback
>> FM60; and a roof-mounted 4kW array feeding the grid panel via the
>> IG-4000. As currently installed, nothing will operate as wired during
>> a grid outage, and a 240V AC well pump isn't supported.
>>
>> The simple plan is to replace the SW5548 with an XW+5548 or 6848 with
>> Midnite E-Panel; replace batteries with Surrette FLAs; keep existing
>> arrays unchanged; use existing FM60 for smaller tracked array; use
>> existing Fronius IG-4000 but AC couple it to the output of the XW.
>> The customer understands that sell amperage is limited by the
>> inverter (to 20A @ 240V for the 5548, or 4,800W, or 27A @ 240V for
>> the 6848, or 6,480W) when the grid is up, but the full array can
>> charge the battery bank when the grid is down.
>>
>> Schneider tech support assures me that the XW+ is good in this
>> application, but I need to get an OK from Fronius about
>> frequency-shift compatibility. Fronius tech support tells me that it
>> may or may not work: the 0.4 hz shift is within the the normal
>> frequency tolerance for this model. While the tolerance window may be
>> tightened up in the field, such tightening may cause nuisance
>> tripping, especially with reactive loads like a well pump or A/C. The
>> tech suggested that we first test the frequency-shift approach, and
>> add a DC-coil contactor between the output of the Fronius and the XW+
>> if it doesn't.
>>
>> Has anyone AC coupled these two units? Did it work? Any unexpected
>> problems? Did you add a voltage-controlled contactor? What should I
>> advise my client?
>> Thank you,
>> Allan
>> --
>> *Allan Sindelar*
>> allan at sindelarsolar.com
>> NABCEP Certified PV Installation Professional
>> NABCEP Certified Technical Sales Professional
>> New Mexico EE98J Journeyman Electrician
>> Founder (Retired),Positive Energy, Inc.
>> *505 780-2738 cell*
>>
>> **
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address:RE-wrenches at lists.re-wrenches.org
>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> <http://www.re-wrenches.org/etiquette.htm>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160404/a6157df6/attachment.html>
More information about the RE-wrenches
mailing list