[RE-wrenches] Wire nuts

Jerry Shafer jerrysgarage01 at gmail.com
Tue Sep 6 11:32:16 PDT 2016


Wrenches
Better pic

On Sep 5, 2016 4:52 PM, "Jerry Shafer" <jerrysgarage01 at gmail.com> wrote:

> To my fellow wrenches
> It comes up every so often and with DC, I will not use, approve or pass
> any wire nuts on any DC side. Some say its OK but the facts are they will
> fail, this connection was just six years and when l opened the junction box
> it was glowing and by the looks of it has for some time. There are 8
> strings 2 per string and thats a 12.5 % failure rate (the other one was
> completely distroyed) not to mention the fire hazard in a PVC junction box.
> Please pass this along and tell everyone to stop using these.
> Jerry
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160906/fc976f9d/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 2016-09-06 08.29.40.jpg
Type: image/jpeg
Size: 302617 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160906/fc976f9d/attachment-0001.jpg>


More information about the RE-wrenches mailing list