[RE-wrenches] Odd battery problem - very low SG in only one cell

Jay jay.peltz at gmail.com
Sun Nov 22 07:08:35 PST 2015


Hi dan

Assuming all charge settings correct, it's a manufacturing fault. 
I couldn't tell if the other lower SG readings were in the same battery or not. 

I just replaced a 1 yr old HUP, cell. 

Now as to what, why, how it failed, that's a good mystery

Jay





> On Nov 22, 2015, at 6:49 AM, Dan Fink <danbob88 at gmail.com> wrote:
> 
> Esteemed Wrenches;
> 
> I'm looking for input on what could be going on with a battery bank at the college I teach for. It's a stand-alone system with 4 Trojan 12v T-1275 in series / parallel for 24v, 660w of PV, running only a drainback solar hot water system for space heating. So, 3 pumps and 3 DTCs, max load 100 watts and doesn't run all that often, outback CC is usually in float. The batteries are only 2.5 years old and are regularly maintained.
> 
> My lab class tested and maintained the battery bank last week, and on one battery there was one cell, in the middle of the battery, with a SG so low it wouldn't even register on our refractometer or midnite hydrometer. That battery reads about 0.2v lower than the others. All the other cells in that battery read reasonable SG, with 2 cells on the downstream side reading SG slightly low, but still in reasonable range. This was of course all before topping up the electrolyte with distilled water.
> 
> Our troubleshooting exercise looked at:
> ~ Measurement error? Nope, I was right there supervising and 2 different lab classes got the same results with 2 different instruments;
> ~ Stratification? A suspicion especially since the system is usually in float. We equalized twice, no change in SG. I DID hear that likely this was the first time the batteries had ever been equalized, but no way to know for sure.
> ~ Spilled electrolyte from tipped battery replaced with water by a previous instructor's class? Can't see this, all the other cells would have lost electrolyte too;
> ~ A student accidentally discharged electrolyte into the bucket instead of back in the cell, then was replaced by distilled water when topping up? I can't see that either, the midnite hydrometer needs only a small sample.
> 
> So, I'm left with "likely we have a cell that is failing for some reason" and students secretly smug that the professor is also stumped.
> 
> Any ideas?
> 
> 
> Dan Fink
> Adjunct Professor, Ecotech Institute
> IREC Certified Instructor™ for: 
> ~ PV Installation Professional
> ~ Small Wind Installer
> Executive Director, Buckville Energy
> NABCEP Accredited Continuing Education Providers™
> 970.672.4342
> 
>  
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20151122/f8e830ab/attachment-0002.html>


More information about the RE-wrenches mailing list