How many basements, utility rooms etc. have conductors that fail the
ground mounted solar array test? I hope the live parts is what is
protected and not the conductors themselves.
On 9/10/2015 7:32 PM, William Miller wrote:
> Ray:
>
> I apologize but I thought this discussion was off-line.
>
> Mike Holy and everyone but apparently our local AHJ agree: wire
> guarding is required.
>
> William
>
>
>
> On Sep 10, 2015, at 4:04 PM, Ray Walters <ray at solarray.com
> <mailto:ray at solarray.com>> wrote:
>
>> I'm confused again. Do we need to guard ground mount arrays or not?
>> I thought it was clear that we did need to guard the array wiring.
>>
>> R.Ray Walters
>> CTO, Solarray, Inc
>> Nabcep Certified PV Installer,
>> Licensed Master Electrician
>> Solar Design Engineer
>> 303 505-8760
>> On 9/9/2015 6:46 PM, William Miller wrote:
>>>
>>> Bill:
>>>
>>> How right you are. I spoke with Mike Stoker of the County of San
>>> Luis Obispo today and he told me that both you and Mike Holt are
>>> saying that guards are not required on readily accessible wiring. I
>>> sent him your recent email to me on the subject. He may be in
>>> touch. If you want to write him, his email is mstoker at co.slo.ca.us
>>> <mailto:mstoker at co.slo.ca.us>.
>>>
>>> I looked on Mike Holt’s site and did not see anything from Mike
>>> about wire guarding. I wrote to Mike and asked him directly. I
>>> will let you know what I learn.
>>>
>>> William
>>>
>>> <mime-attachment.jpg>
>>> Lic 773985
>>> millersolar.com <http://www.millersolar.com/>
>>> 805-438-5600
>>>
>>> *From:*RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org
>>> <mailto:re-wrenches-bounces at lists.re-wrenches.org>] *On Behalf Of
>>> *billbrooks7 at sbcglobal.net <mailto:billbrooks7 at sbcglobal.net>
>>> *Sent:* Saturday, September 05, 2015 2:21 PM
>>> *To:* 'RE-wrenches'
>>> *Subject:* Re: [RE-wrenches] Guarding against live parts 690.7 (D)
>>>
>>> William,
>>>
>>> You can always quote me to an AHJ, as long as I actually said it or
>>> wrote it.
>>>
>>> I have been accused of saying all kinds of things that I never
>>> said—people just misunderstood what I said and “quoted” me incorrectly.
>>>
>>> All the best—and stay safe. Always tragic to hear of
>>> electrocutions—most are so preventable as this one clearly was.
>>> Never, ever assume that a circuit is off. I know you warned against
>>> inductive sensors, but they should still be used as one of several
>>> methods to detect voltage. I just watched a video about a guy who
>>> thought he was testing a 480V circuit when it was really a 12kV
>>> circuit. The fireball caught him on fire and burned him to death.
>>> The meter was the problem. An inductive sensor would have saved his
>>> life. There is no single method for safety.
>>>
>>> Bill.
>>>
>>> *From:*RE-wrenches
>>> [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of
>>> *William Miller
>>> *Sent:* Friday, September 04, 2015 2:37 PM
>>> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org
>>> <mailto:re-wrenches at lists.re-wrenches.org>>
>>> *Subject:* Re: [RE-wrenches] Guarding against live parts 690.7 (D)
>>>
>>> Bill:
>>>
>>> I apologize that I assumed incorrectly. Thank you for your
>>> assessment. May I quote you to our AHJ?
>>>
>>> Sincerely,
>>>
>>> William
>>>
>>> Gradient Cap_mini
>>> Lic 773985
>>> millersolar.com <http://www.millersolar.com/>
>>> 805-438-5600
>>>
>>> *From:*RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org
>>> <mailto:re-wrenches-bounces at lists.re-wrenches.org>] *On Behalf Of
>>> *billbrooks7 at sbcglobal.net <mailto:billbrooks7 at sbcglobal.net>
>>> *Sent:* Friday, September 04, 2015 12:59 PM
>>> *To:* 'RE-wrenches'
>>> *Subject:* Re: [RE-wrenches] Guarding against live parts 690.7 (D)
>>>
>>> William,
>>>
>>> I’m shocked and offended (a tiny bit) that you would prejudice
>>> yourself to not agree with me ;-).
>>>
>>> First of all I have been heavily involved in the revising of the
>>> language in 690.31(A) to make it clear that we cannot walk up and
>>> touch cables operating at 600V. The term guarded is a defined term:
>>>
>>> *Guarded. *Covered, shielded, fenced, enclosed, or otherwise
>>>
>>> protected by means of suitable covers, casings, barriers,
>>>
>>> rails, screens, mats, or platforms to remove the likelihood
>>>
>>> of approach or contact by persons or objects to a point
>>>
>>> of danger.
>>>
>>> A fence actually does not prevent ready access (unless it does not
>>> have a gate), but the term guarded fixes that problem. The guarding
>>> means has to be approved by the AHJ, but many methods have been
>>> employed including mounting lattice work around the backside of
>>> fixed ground-mounted systems.
>>>
>>> Fences are best used for larger systems (over 50-100kW) whereas
>>> other methods—albeit labor intensive—are generally preferred for
>>> smaller installations (under 100 kW)
>>>
>>> No intelligent person would disagree with this proper interpretation
>>> of the NEC—including you.
>>>
>>> Bill.
>>>
>>> *From:*RE-wrenches
>>> [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of
>>> *William Miller
>>> *Sent:* Friday, September 04, 2015 12:09 PM
>>> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org
>>> <mailto:re-wrenches at lists.re-wrenches.org>>
>>> *Subject:* Re: [RE-wrenches] Guarding against live parts 690.7 (D)
>>>
>>> Ray:
>>>
>>> 1.Why no fence? Aesthetics. Also costs may be a wash by the time
>>> you mobilize a fencing contractor.
>>>
>>> 2.I’d apply the same requirements to a fence as one would to an
>>> uncovered swimming pool. There are the same consequences if a child
>>> ends up in the wrong place.
>>>
>>> 3.Why bother?
>>>
>>> We figure the expense will decrease as we figure better design and
>>> implementation. Hasn’t yet.
>>>
>>> We care about safety. I figure we, as an industry, will kill a
>>> child by electrocution someday—it is a matter of probability. I
>>> hope it won’t be on one of our jobs.
>>>
>>> We hope, in some small way, we influence the industry to improve.
>>>
>>> 4.The industry has not developed solutions because there is no
>>> demand. There is no demand because AHJs don’t enforce the code.
>>>
>>> Thanks for the compliment. We have several new designs not yet
>>> featured on the web site. Check back next time this comes up.
>>>
>>> William
>>>
>>> PS: I am curious what Bill Brooks take on this is, but I don’t think
>>> I will agree with his interpretation.
>>>
>>> W
>>>
>>> Gradient Cap_mini
>>> Lic 773985
>>> millersolar.com <http://www.millersolar.com/>
>>> 805-438-5600
>>>
>>> *From:*RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org
>>> <mailto:re-wrenches-bounces at lists.re-wrenches.org>] *On Behalf Of
>>> *Ray Walters
>>> *Sent:* Friday, September 04, 2015 11:37 AM
>>> *To:* RE-wrenches
>>> *Subject:* Re: [RE-wrenches] Guarding against live parts 690.7 (D)
>>>
>>> WilIiam;
>>>
>>> checked out your guards on your website, that looks really clean,
>>> but also like a lot of work and expense. I'm still so surprised
>>> manufacturers are not offering an option like that to their frame
>>> systems.
>>> My question: how come you didn't just fence the array? Shading
>>> issues on the south?
>>> If fencing, what height of fence is considered adequate? 4 ft? 6 ft?
>>>
>>> R.Ray Walters
>>> CTO, Solarray, Inc
>>> Nabcep Certified PV Installer,
>>> Licensed Master Electrician
>>> Solar Design Engineer
>>> 303 505-8760
>>>
>>> On 9/4/2015 9:44 AM, William Miller wrote:
>>>
>>> Gary:
>>>
>>> I think the issue of PV wiring behind module that are readily
>>> accessible is addressed in (2014) 690.31:
>>>
>>> /Where PV source and output circuits operating at maximum/
>>>
>>> /system voltages greater than 30 volts are installed in/
>>>
>>> /readily accessible locations, circuit conductors shall be/
>>>
>>> /guarded or installed in a raceway./
>>>
>>> I am not sure what application the original poster had in mind,
>>> but this is the question I think you are asking. The
>>> interpretation to 690.31 seems clear to me: No one should be
>>> able to touch the conductors without resorting to a ladder,
>>> opening a locked gate or removing a protective panel. Readily
>>> accessible is defined thusly:
>>>
>>> /Capable of being /
>>>
>>> /reached quickly for operation, renewal, or inspections/
>>>
>>> /without requiring those to whom ready access is requisite/
>>>
>>> /to actions such as to use tools, to climb over or remove/
>>>
>>> /obstacles, or to resort to portable ladders, and so forth./
>>>
>>> Implementing this is harder than it might seem. Lacking a
>>> fence, the installer must either use the flimsy solar-scrim
>>> product or fabricate his or her own shielding. We have put a
>>> fair amount of effort towards this. See link
>>> <http://www.millersolar.com/MillerSolar/practices/PV_wiring/Wire_shielding/_Wire%20Shielding_history.html>.
>>>
>>> William
>>>
>>> Gradient Cap_mini
>>> Lic 773985
>>> millersolar.com <http://www.millersolar.com/>
>>> 805-438-5600
>>>
>>> *From:*RE-wrenches
>>> [mailto:re-wrenches-bounces at lists.re-wrenches.org
>>> <mailto:re-wrenches-bounces at lists.re-wrenches.org>] *On Behalf
>>> Of *gary easton
>>> *Sent:* Friday, September 04, 2015 2:22 AM
>>> *To:* RE-wrenches
>>> *Subject:* Re: [RE-wrenches] Guarding against live parts 690.7 (D)
>>>
>>> Bill
>>>
>>> Are you saying there is no requirement to shield wires on a
>>> ground array?
>>>
>>> On Friday, September 4, 2015, <billbrooks7 at sbcglobal.net> wrote:
>>>
>>> Craig,
>>>
>>> This one is easy to misinterpret. You missed the words “live
>>> parts”. This has been removed from the 2017 NEC because it is
>>> actually referring to load circuits being fed directly by a PV
>>> system on the dc side. All references to loads and batteries are
>>> being removed from 690.
>>>
>>> This is a complete non-issue.
>>>
>>> Bill.
>>>
>>> *From:*RE-wrenches
>>> [mailto:re-wrenches-bounces at lists.re-wrenches.org
>>> <javascript:_e(%7B%7D,'cvml','re-wrenches-bounces at lists.re-wrenches.org');>]
>>> *On Behalf Of *Craig Gerald Buttke
>>> *Sent:* Thursday, September 03, 2015 11:44 AM
>>> *To:* re-wrenches at lists.re-wrenches.org
>>> <javascript:_e(%7B%7D,'cvml','re-wrenches at lists.re-wrenches.org');>
>>> *Subject:* [RE-wrenches] Guarding against live parts 690.7 (D)
>>>
>>>
>>>
>>> How is everyone handling 690.7 (D)
>>>
>>> *Circuits over 150 Volts to Ground. *In one- and two- family
>>> dwellings, live parts in photovoltaic source circuits and
>>> photovoltaic output circuits over 150 volts to ground shall not
>>> be accessible to other than qualified persons while energized.
>>>
>>>
>>>
>>> If you have a commercial (non one or two-family dwelling) are
>>> you screening your ground mount arrays to keep people from
>>> touching live conductors PV wires)?
>>>
>>> Thanks for your thoughts
>>>
>>> --
>>>
>>> Yours in Solardarity,
>>>
>>>
>>>
>>> Craig Gerald Buttke
>>>
>>>
>>>
>>> M:(715) 630-1227
>>>
>>> O:(715) 630-6451
>>>
>>> F:(715) 952-4501
>>>
>>>
>>>
>>> North Wind Renewable Energy, LLC
>>>
>>> 1626C W Pearl Street
>>>
>>> Stevens Point, WI 54481
>>>
>>>
>>>
>>> www.northwindre.com <http://www.northwindre.com>
>>>
>>>
>>>
>>> NABCEP Certified PV Installation Professional™
>>>
>>> NABCEP Certified PV Technical Sales Professional™
>>>
>>> State of WI: Master Electrician
>>>
>>> ------------------------------------------------------------------------
>>>
>>> Avast logo <https://www.avast.com/antivirus>
>>>
>>>
>>>
>>> This email has been checked for viruses by Avast antivirus
>>> software.
>>> www.avast.com <https://www.avast.com/antivirus>
>>>
>>>
>>>
>>> --
>>> Sent from Gmail Mobile
>>>
>>> _______________________________________________
>>>
>>> List sponsored by Redwood Alliance
>>>
>>>
>>>
>>> List Address:RE-wrenches at lists.re-wrenches.org
>>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>>
>>>
>>>
>>> Change listserver email address & settings:
>>>
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>>
>>>
>>> List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>>
>>>
>>> List rules & etiquette:
>>>
>>> www.re-wrenches.org/etiquette.htm
>>> <http://www.re-wrenches.org/etiquette.htm>
>>>
>>>
>>>
>>> Check out or update participant bios:
>>>
>>> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>>
>>>
>>>
>>> ------------------------------------------------------------------------
>>>
>>> Avast logo <https://www.avast.com/antivirus>
>>>
>>>
>>>
>>> This email has been checked for viruses by Avast antivirus software.
>>> www.avast.com <https://www.avast.com/antivirus>
>>>
>>> ------------------------------------------------------------------------
>>>
>>> Avast logo <https://www.avast.com/antivirus>
>>>
>>>
>>>
>>> This email has been checked for viruses by Avast antivirus software.
>>> www.avast.com <https://www.avast.com/antivirus>
>>>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address:RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> <http://www.re-wrenches.org/etiquette.htm>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
--
Christopher Warfel, President
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
401-466-8978
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150915/3594ed09/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1460 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150915/3594ed09/attachment-0002.jpe>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: cwarfel.vcf
Type: text/x-vcard
Size: 100 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150915/3594ed09/attachment-0004.vcf>
More information about the RE-wrenches
mailing list