[RE-wrenches] Guarding against live parts 690.7 (D)

Ray Walters ray at solarray.com
Thu Sep 10 16:04:59 PDT 2015


I'm confused again.  Do we need to guard ground mount arrays or not?  I 
thought it was clear that we did need to guard the array wiring.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 9/9/2015 6:46 PM, William Miller wrote:
>
> Bill:
>
> How right you are.  I spoke with Mike Stoker of the County of San Luis 
> Obispo today and he told me that both you and Mike Holt are saying 
> that guards are not required on readily accessible wiring.  I sent him 
> your recent email to me on the subject.  He may be in touch.  If you 
> want to write him, his email is mstoker at co.slo.ca.us 
> <mailto:mstoker at co.slo.ca.us>.
>
> I looked on Mike Holt’s site and did not see anything from Mike about 
> wire guarding.  I wrote to Mike and asked him directly.  I will let 
> you know what I learn.
>
> William
>
> Gradient Cap_mini
> Lic 773985
> millersolar.com <http://www.millersolar.com/>
> 805-438-5600
>
> *From:*RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org 
> <mailto:re-wrenches-bounces at lists.re-wrenches.org>] *On Behalf Of 
> *billbrooks7 at sbcglobal.net <mailto:billbrooks7 at sbcglobal.net>
> *Sent:* Saturday, September 05, 2015 2:21 PM
> *To:* 'RE-wrenches'
> *Subject:* Re: [RE-wrenches] Guarding against live parts 690.7 (D)
>
> William,
>
> You can always quote me to an AHJ, as long as I actually said it or 
> wrote it.
>
> I have been accused of saying all kinds of things that I never 
> said—people just misunderstood what I said and “quoted” me incorrectly.
>
> All the best—and stay safe. Always tragic to hear of 
> electrocutions—most are so preventable as this one clearly was. Never, 
> ever assume that a circuit is off. I know you warned against inductive 
> sensors, but they should still be used as one of several methods to 
> detect voltage. I just watched a video about a guy who thought he was 
> testing a 480V circuit when it was really a 12kV circuit. The fireball 
> caught him on fire and burned him to death. The meter was the problem. 
> An inductive sensor would have saved his life. There is no single 
> method for safety.
>
> Bill.
>
> *From:*RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] 
> *On Behalf Of *William Miller
> *Sent:* Friday, September 04, 2015 2:37 PM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org 
> <mailto:re-wrenches at lists.re-wrenches.org>>
> *Subject:* Re: [RE-wrenches] Guarding against live parts 690.7 (D)
>
> Bill:
>
> I apologize that I assumed incorrectly.  Thank you for your 
> assessment.  May I quote you to our AHJ?
>
> Sincerely,
>
> William
>
> Gradient Cap_mini
> Lic 773985
> millersolar.com <http://www.millersolar.com/>
> 805-438-5600
>
> *From:*RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org 
> <mailto:re-wrenches-bounces at lists.re-wrenches.org>] *On Behalf Of 
> *billbrooks7 at sbcglobal.net <mailto:billbrooks7 at sbcglobal.net>
> *Sent:* Friday, September 04, 2015 12:59 PM
> *To:* 'RE-wrenches'
> *Subject:* Re: [RE-wrenches] Guarding against live parts 690.7 (D)
>
> William,
>
> I’m shocked and offended (a tiny bit) that you would prejudice 
> yourself to not agree with me ;-).
>
> First of all I have been heavily involved in the revising of the 
> language in 690.31(A) to make it clear that we cannot walk up and 
> touch cables operating at 600V. The term guarded is a defined term:
>
> *Guarded. *Covered, shielded, fenced, enclosed, or otherwise
>
> protected by means of suitable covers, casings, barriers,
>
> rails, screens, mats, or platforms to remove the likelihood
>
> of approach or contact by persons or objects to a point
>
> of danger.
>
> A fence actually does not prevent ready access (unless it does not 
> have a gate), but the term guarded fixes that problem. The guarding 
> means has to be approved by the AHJ, but many methods have been 
> employed including mounting lattice work around the backside of fixed 
> ground-mounted systems.
>
> Fences are best used for larger systems (over 50-100kW) whereas other 
> methods—albeit labor intensive—are generally preferred for smaller 
> installations (under 100 kW)
>
> No intelligent person would disagree with this proper interpretation 
> of the NEC—including you.
>
> Bill.
>
> *From:*RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] 
> *On Behalf Of *William Miller
> *Sent:* Friday, September 04, 2015 12:09 PM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org 
> <mailto:re-wrenches at lists.re-wrenches.org>>
> *Subject:* Re: [RE-wrenches] Guarding against live parts 690.7 (D)
>
> Ray:
>
> 1.Why no fence?  Aesthetics.  Also costs may be a wash by the time you 
> mobilize a fencing contractor.
>
> 2.I’d apply the same requirements to a fence as one would to an 
> uncovered swimming pool.  There are the same consequences if a child 
> ends up in the wrong place.
>
> 3.Why bother?
>
> We figure the expense will decrease as we figure better design and 
> implementation.  Hasn’t yet.
>
> We care about safety.  I figure we, as an industry, will kill a child 
> by electrocution someday—it is a matter of probability.  I hope it 
> won’t be on one of our jobs.
>
> We hope, in some small way, we influence the industry to improve.
>
> 4.The industry has not developed solutions because there is no demand. 
> There is no demand because AHJs don’t enforce the code.
>
> Thanks for the compliment.  We have several new designs not yet 
> featured on the web site. Check back next time this comes up.
>
> William
>
> PS: I am curious what Bill Brooks take on this is, but I don’t think I 
> will agree with his interpretation.
>
> W
>
> Gradient Cap_mini
> Lic 773985
> millersolar.com <http://www.millersolar.com/>
> 805-438-5600
>
> *From:*RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org 
> <mailto:re-wrenches-bounces at lists.re-wrenches.org>] *On Behalf Of *Ray 
> Walters
> *Sent:* Friday, September 04, 2015 11:37 AM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Guarding against live parts 690.7 (D)
>
> WilIiam;
>
>  checked out your guards on your website, that looks really clean, but 
> also like a lot of work and expense.  I'm still so surprised 
> manufacturers are not offering an option like that to their frame systems.
> My question: how come you didn't just fence the array? Shading issues 
> on the south?
> If fencing, what height of fence is considered adequate?  4 ft?  6 ft?
>
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer,
> Licensed Master Electrician
> Solar Design Engineer
> 303 505-8760
>
> On 9/4/2015 9:44 AM, William Miller wrote:
>
>     Gary:
>
>     I think the issue of PV wiring behind module that are readily
>     accessible is addressed in (2014) 690.31:
>
>     /Where PV source and output circuits operating at maximum/
>
>     /system voltages greater than 30 volts are installed in/
>
>     /readily accessible locations, circuit conductors shall be/
>
>     /guarded or installed in a raceway./
>
>     I am not sure what application the original poster had in mind,
>     but this is the question I think you are asking. The
>     interpretation to 690.31 seems clear to me:  No one should be able
>     to touch the conductors without resorting to a ladder, opening a
>     locked gate or removing a protective panel.  Readily accessible is
>     defined thusly:
>
>     /Capable of being /
>
>     /reached quickly for operation, renewal, or inspections/
>
>     /without requiring those to whom ready access is requisite/
>
>     /to actions such as to use tools, to climb over or remove/
>
>     /obstacles, or to resort to portable ladders, and so forth./
>
>     Implementing this is harder than it might seem.  Lacking a fence,
>     the installer must either use the flimsy solar-scrim product or
>     fabricate his or her own shielding.  We have put a fair amount of
>     effort towards this.  See link
>     <http://www.millersolar.com/MillerSolar/practices/PV_wiring/Wire_shielding/_Wire%20Shielding_history.html>.
>
>     William
>
>     Gradient Cap_mini
>     Lic 773985
>     millersolar.com <http://www.millersolar.com/>
>     805-438-5600
>
>     *From:*RE-wrenches
>     [mailto:re-wrenches-bounces at lists.re-wrenches.org
>     <mailto:re-wrenches-bounces at lists.re-wrenches.org>] *On Behalf Of
>     *gary easton
>     *Sent:* Friday, September 04, 2015 2:22 AM
>     *To:* RE-wrenches
>     *Subject:* Re: [RE-wrenches] Guarding against live parts 690.7 (D)
>
>     Bill
>
>     Are you  saying there is no requirement to shield wires on a
>     ground array?
>
>     On Friday, September 4, 2015, <billbrooks7 at sbcglobal.net
>     <mailto:billbrooks7 at sbcglobal.net>> wrote:
>
>     Craig,
>
>     This one is easy to misinterpret. You missed the words “live
>     parts”. This has been removed from the 2017 NEC because it is
>     actually referring to load circuits being fed directly by a PV
>     system on the dc side. All references to loads and batteries are
>     being removed from 690.
>
>     This is a complete non-issue.
>
>     Bill.
>
>     *From:*RE-wrenches
>     [mailto:re-wrenches-bounces at lists.re-wrenches.org
>     <javascript:_e(%7B%7D,'cvml','re-wrenches-bounces at lists.re-wrenches.org');>]
>     *On Behalf Of *Craig Gerald Buttke
>     *Sent:* Thursday, September 03, 2015 11:44 AM
>     *To:* re-wrenches at lists.re-wrenches.org
>     <javascript:_e(%7B%7D,'cvml','re-wrenches at lists.re-wrenches.org');>
>     *Subject:* [RE-wrenches] Guarding against live parts 690.7 (D)
>
>
>
>     How is everyone handling 690.7 (D)
>
>     *Circuits over 150 Volts to Ground. *In one- and two- family
>     dwellings, live parts in photovoltaic source circuits and
>     photovoltaic output circuits over 150 volts to ground shall not be
>     accessible to other than qualified persons while energized.
>
>
>
>     If you have a commercial (non one or two-family dwelling) are you
>     screening your ground mount arrays to keep people from touching
>     live conductors PV wires)?
>
>     Thanks for your thoughts
>
>     -- 
>
>     Yours in Solardarity,
>
>       
>
>     Craig Gerald Buttke
>
>       
>
>     M:(715) 630-1227
>
>     O:(715) 630-6451
>
>     F:(715) 952-4501
>
>       
>
>     North Wind Renewable Energy, LLC
>
>     1626C W Pearl Street
>
>     Stevens Point, WI 54481
>
>       
>
>     www.northwindre.com <http://www.northwindre.com>
>
>       
>
>     NABCEP Certified PV Installation Professional™
>
>     NABCEP Certified PV Technical Sales Professional™
>
>     State of WI: Master Electrician
>
>     ------------------------------------------------------------------------
>
>     Avast logo <https://www.avast.com/antivirus>
>
>     	
>
>     This email has been checked for viruses by Avast antivirus software.
>     www.avast.com <https://www.avast.com/antivirus>
>
>
>
>     -- 
>     Sent from Gmail Mobile
>
>     _______________________________________________
>
>     List sponsored by Redwood Alliance
>
>       
>
>     List Address:RE-wrenches at lists.re-wrenches.org
>     <mailto:RE-wrenches at lists.re-wrenches.org>
>
>       
>
>     Change listserver email address & settings:
>
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>       
>
>     List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>       
>
>     List rules & etiquette:
>
>     www.re-wrenches.org/etiquette.htm
>     <http://www.re-wrenches.org/etiquette.htm>
>
>       
>
>     Check out or update participant bios:
>
>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>       
>
> ------------------------------------------------------------------------
>
> Avast logo <https://www.avast.com/antivirus>
>
> 	
>
> This email has been checked for viruses by Avast antivirus software.
> www.avast.com <https://www.avast.com/antivirus>
>
> ------------------------------------------------------------------------
>
> Avast logo <https://www.avast.com/antivirus>
>
> 	
>
> This email has been checked for viruses by Avast antivirus software.
> www.avast.com <https://www.avast.com/antivirus>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150910/09d45b8d/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1460 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150910/09d45b8d/attachment-0004.jpe>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1460 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150910/09d45b8d/attachment-0005.jpe>


More information about the RE-wrenches mailing list