Ray

  Couple of thoughts on your application. We used to use the sunny islands a 
lot, challenge is they are only 120 volt so we needed to have two or add a 
transformer, which proved problematic with the grid tied inverters and hertz 
ranges.

  So now we use the Outback 4048 and 8048 radians ( 8048 cost close to the 
same as a Sunny Island ) is 240, no transformer needed and a simple relay to 
break the main neutral on the enphases will shut them off when the voltage 
goes too high if the grid goes down and there is no load.

  Outback also has their load center that has the circuitry built in to shut 
off the enphases. Keep it all ac, make it an AC coupled application, the 
enphases should work very well partnered with the radians. The radian hooks 
to the main service panel on AC in. AC out runs to the critical loads panel 
and you can run the enphase system right into the critical loads panel. 
While power is up the system works just like a grid tied system with the 
battery portion and radian in standby. When the power goes down, not a 
flinch, everything in the critical loads panel is hot, with the battery 
system and the grid tied system. Very nice setup

peter giroux
ASAE


----- Original Message ----- 
From: "Ray Walters" <ray at solarray.com>
To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
Sent: Monday, August 17, 2015 4:10 PM
Subject: [RE-wrenches] AC Coupled with Generator


> HI Esteemed Wrenches:
>
> I am consulting on a system I have never seen, that consists of a 6.7Kw 
> Enphase roof mounted system, and 2 backup generators.  Each generator has 
> an automatic 200 amp transfer switch to back up its own 200 amp panel. 
> Both 200 amp panels are fed by a 400 amp service from the grid.
> The Enphase PV backfeeds a subpanel in another building which then is fed 
> by a 2 pole 60 amp breaker in one of the 200 amp panels.
> Currently they are having issues with the generators kicking out because 
> of the Enphase inverters.  That part I understand: you can't backfeed a 
> generator, or its voltage regulation freaks out.
>
> Now we get to the fun part: they want to create a third critical load 
> subpanel with loads selected from both 200 amp panels to be powered by 
> batteries and an inverter.
> I am considering the Sunny Island since it makes the most sense with its 
> ability to signal the Enphase inverters to shut off when the batteries are 
> full.  I also see this as a partial solution to the generator issue, since 
> normally the Enphase will be connected to the output side of the Sunny 
> Island.  However, when the generator is used to charge, we will be back to 
> directly coupling the generator output to the Enphase.
>
> Here are some possible solutions I'm considering:
> 1) Use a separate charger for the generator so that it will only feed DC 
> to the batteries, and not be AC coupled.
> 2) convert the PV back to DC with charge controllers, but that would 
> involve ditching and adding another conduit run between buildings.
> 3)  Put the Enphase PV on a relay that would disconnect the PV when 
> charging with the generator.
> 4) Something I haven't thought of that one of you clever folks can 
> suggest......
>
> As always, thanks in advance for all you responses,
>
> -- 
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer,
> Licensed Master Electrician
> Solar Design Engineer
> 303 505-8760
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> 




More information about the RE-wrenches mailing list