Going back many many years, twisting the pairs together was the preferred
way to run the cables between the inverter and batteries, this seamed to
reduce noise, I have personally seen improvement of audio conditions. Doing
this on the AC side does the opposite and creates noise on sound mixers and
powered amps.
Jerry

On Fri, Jun 26, 2015 at 7:45 AM, <Jarmo.Venalainen at schneider-electric.com>
wrote:

> Hi:
>
> From time to time over the years I've come across systems where the
> routing of DC cables between the batteries and the inverter has been the
> cause of  issues.
>
> I'm not referring to wire thickness or quality of terminations.  For the
> purposes of this discussion, just assume that wire thickness and
> terminations are perfect.
>
> What I am referring to is the routing of the positive and negative battery
> cables.  In particular, the loop area within the + and - cables as shown in
> the image below,
>
>
> The problem I've seen in systems with a large loop in the setup is that
> the inverter does not provide good surge power and can even go into low
> voltage shutdown during large surges.
>
> Recently this happened again and I wanted to get a better feel for it, so
> I did some math.
>
> For a cable length of about 12', the loop is an inductor which has a value
> of inductance of about 1 uH for side by side cables and as much as 6 uH for
> cables about 1 foot apart.
>
> This inductance is greatly multiplied by any ferrous metal in the loop and
> can easily be in the range of 10's to 100's of uH.  Examples being cables
> which run in steel conduits or along the steel frame of a motor home.
>
> Inductance causes a voltage drop proportional to the rate at which the
> current is changing.  To get an idea of how large that rate can be for
> typical inverters, I did surge tests with a 5kW inverter and found that the
> rate of change of current can be as high as 100A per milli-second or
> 100,000 Amps/second.
>
> Given that, the voltage drop of the wire inductance is then , Vdrop =
> (rate of change of current) x (inductance),
>
> Vdrop for 1 uH = (100,000 A/s) x (0.000001 H) = 0.1V
> Vdrop for 10 uH = (100,000 A/s) x (0.000001 H) = 1.0V
> Vdrop for 100 uH = (100,000 A/s) x (0.000001 H) = 10.0V    clearly this is
> a problem.
>
> Have any of the wrenches had systems with this issue?  If so, how often.
>
>
> JARMO
>
>
>
>
> _____________________________________________________________________________________
>
> * Jarmo Venalainen*  |  * Schneider Electric **  |  Xantrex Brand*  |
> *CANADA*  |   *Sales Application Engineer*
> * Phone:* +604-422-2528  |   *Tech Support:* 800-670-0707  |   *Mobile:*
> +604-505-0291
> * Email:* *jarmo.venalainen at schneider-electric.com*
> <jarmo.venalainen at schneider-electric.com>  |   *Site:** www.Xantrex.com*
> <http://www.xantrex.com/>  |   *Address:* 3700 Gilmore Way, Burnaby, BC
> V5G4M1
>   <http://www.xantrexrebate.com/>  <http://www.xantrex.com/>
> <https://www.facebook.com/Xantrex> <https://twitter.com/Xantrex>
> <https://twitter.com/Xantrex>
>
>
> *** Please consider the environment before printing this e-mail
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150626/811662ea/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 1897 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150626/811662ea/attachment-0024.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 4274 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150626/811662ea/attachment-0025.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 14647 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150626/811662ea/attachment-0026.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 1869 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150626/811662ea/attachment-0027.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 2041 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150626/811662ea/attachment-0028.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 40194 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150626/811662ea/attachment-0029.gif>


More information about the RE-wrenches mailing list