Why not use an IOTA 48V plug in battery charger? In a backup situation, the
TL can output at 120V up to 1500W, should be enough to help out.
Mike

On Sun, Jun 7, 2015 at 9:38 AM, Jerry Shafer <jerrysgarage01 at gmail.com>
wrote:

> No, however you will need to keep the tl charger input demand well within
> the tl capability. There are a lot of 48 volt golf cart chargers out there
> but most are fixed output.
> You might consider AC coupling the tl to the Radian skip the charger
> altogether. Just a thhought.
> On Jun 7, 2015 5:53 AM, "gary easton" <gary at arp-solar.com> wrote:
>
>> I have a customer with an outback Radian system as well as an SMA TL
>> inverter.  He would like to plug a small battery charger into the emergency
>> outlet on the SMA if the grid goes down and send that little extra juice
>> into his battery bank.  Is there an issue with two systems charging the
>> same bank?
>>
>> --
>> Sent from Gmail Mobile
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Michael & Jessica Nelson
MD Electric & Solar Inc.
Office: 707-884-1862
Cell: 707-684-0064
*We prefer to have ALL documentation E-mailed ** prevent paper
waste**please think before you print*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150607/67bea6d1/attachment-0002.html>


More information about the RE-wrenches mailing list