[RE-wrenches] FLA battery setpoints with larger arrays
jay peltz
jay.peltz at gmail.com
Fri May 22 18:43:11 PDT 2015
agreed.
Again, maybe Steve has an view of the builder, but having it on the post is
pretty close.
Maybe there is a white paper on temp sensor locations pros/cons?
jay
On Fri, May 22, 2015 at 5:08 PM, frenergy <frenergy at psln.com> wrote:
> This is good stuff, enlightening...but begs another small? detail that
> has obvious big ramifications. Where o where does the BTS get placed to
> best read the actual "temperature of the battery"? It's too big to fit on
> many terminals especially once cabled, it's certainly not very accurate
> when stuck to the outer case of a dual cased Surrette and probably only
> somewhat more accurate when stuck to an L-16 top. Aren't we looking for
> electrolyte temps?
>
> Many times the BTS doesn't survive its original location after a
> few years of battery acid. Rather than "insulated" from the surface its
> been assigned to with 2-sided tape, it seems like it should be in direct
> contact with that surface with a dab of thermal grease between. Or,
> couldn't a wrench be trusted to drill a 1/4" hole in the top of a
> representative cell and insert an acid proof sensor into the electrolyte
> with a formed snap-in plug (rubber, silicone, nylon??) behind it on the
> lead, to seal it where it enters the battery case?
>
> Just saying, if we really need (and I think we do) accurate
> battery temp for temp regulation and battery health, what we're using now
> is substandard.
>
> Bill
> Feather River Solar Electric
>
> ----- Original Message -----
> *From:* Ray Walters <ray at solarray.com>
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
> *Sent:* Friday, May 22, 2015 3:33 PM
> *Subject:* Re: [RE-wrenches] FLA battery setpoints with larger arrays
>
> I thought I'd post some info on Battery Temp from a few manus:
> HUP Solar One: do not exceed 105 F
> Full River AGMs: max recommended operating temp 104F
> and from Trojan: for every 10C increase in temperature the reaction rate
> doubles. Thus, a month of operation at 35C is equivalent to 2 months at
> 25C. Heat is the enemy of ALL lead acid batteries. Even small increases
> in temperature will have a major influence on battery life.
> Their T105 RE battery has a max operating temperature of 113 F
>
> I think more batteries are hitting high temperatures than we may realize.
> This info from Trojan that a battery at 95F (35C) will only last half its
> rated life (at 25C) is very concerning.
> Once again, thanks Bob and Midnite for giving us a tool to combat over
> temperature of batteries. We always knew cold was a problem, now I'm
> realizing heat could be just as important.
>
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer,
> Licensed Master Electrician
> Solar De
>
> --
Jay Peltz
Peltz Power
jay.peltz at gmail.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150522/b12a49e4/attachment-0002.html>
More information about the RE-wrenches
mailing list