[RE-wrenches] Question on Back up generators

Dana dana at solarwork.com
Thu Apr 9 14:17:53 PDT 2015


I am going out on a limb here - In 26 years of installing generators I have
only seen (2) Generacs that were actually working, one was a 30 KW and the
other smaller. I have removed/replaced in excess of (25) Generacs that have
died for a variety of issues: fire, controller blew up, engine seized
(several times) over that time span.

Primarily because the owners were totally fed up with getting them fixed and
having to rent a temp replacement while the wreck was in the shop. For some
of these people they had to drive 2+ hours each way to get it to an approved
service center. Enough said I will stop there.

 

I am aware of the ECOGen and again it is 2,700 to 3,600 RPM. 3,600 RPM is 80
miles per hour with an air cooled engine.  How do you expect long and
reliable life there?

Interesting on the 2000 hour warranty that seems to be the hour limit on
most air cooled 3,600 rpm unit where they fail, & Oil changes at 40,000
miles exceeds AMSOILs synthetic 25,000 mile best oil rating by 15,000 miles.
However the prior 26 years of experience have taught me to be very careful
here.

 

I am curious as to actual life on these units and other folk's experience.
Chime in here.

 

Still looking & voting for a water cooled slow rpm 10 KW.....

 

 

----------------------------------------------------------------------------

Dana Orzel 

Great Solar Works, Inc -  NABCEP # 051112-136

E - dana at solarwork.com  - Web - solarwork.com 

O - 970.626.5253  C - 208.721.7003

"Responsible Technologies for Responsible People since 1988"  

P Please consider the environment before printing this email.

 

 

From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
Behalf Of Gary Willett
Sent: Thursday, April 09, 2015 2:41 PM
To: re-wrenches at lists.re-wrenches.org
Subject: Re: [RE-wrenches] Question on Back up generators

 

Dana:

Take a look at the new Generac EcoGen 15kW that was purpose built for a
renewable energy system* 
* including an inverter, battery bank and alternative energy power source

http://gens.lccdn.com/generaccorporate/media/library/content/all-products/ge
nerators/home-generators/ecogen-series/15kw-6103/0k8466-c-15kw-ecogen-hsb.pd
f

The 15kW EcoGen has the same footprint as the 6kW EcoGen (LP only) and is
natural gas or LP gas capable. The generator has a constant frequency /
variable speed AVR based on electrical demand. 

Also, 500 run hours between oil changes. And a 3-year or 2000 hour warranty.
http://gens.lccdn.com/generaccorporate/media/library/content/all-products/ge
nerators/home-generators/ecogen-series/ecogen-warranty-0j1629-revb.pdf

Regards,

Gary Willett
Icarus Engineering & Solar Services LLC



On 4/9/15 9:56 AM, Dana wrote:

I agree but full load charging usually only lasts but a few minutes as the
inverter charge rate drops readily as voltage rises. 8300 watt -10,000 watts
or 13000 watts the point is why we are installing air cooled throw away
generators that run so fast & hot that they need to be replaced in 2,000
hours, not to mention the fuel consumed at 80 MPH?

 

Is there a slow speed (1200-1800 rpm) water cooled 8-13 KW generator out
there?

 

----------------------------------------------------------------------------

Dana Orzel 

Great Solar Works, Inc -  NABCEP # 051112-136

E - dana at solarwork.com  - Web - solarwork.com 

O - 970.626.5253  C - 208.721.7003

"Responsible Technologies for Responsible People since 1988"  

P Please consider the environment before printing this email.

 

 

From: Jerry Shafer [mailto:jerrysgarage01 at gmail.com] 
Sent: Wednesday, April 08, 2015 7:02 PM
To: dana at solarwork.com; RE-wrenches
Subject: Re: [RE-wrenches] Question on Back up generators

 

We don't install anything smaller then a 13 k its air cooled but works well,
as far as the numbers you have, Mine are somewhat different I use max
potential load and max potential charge as when the batteries are low the
genny must not only supply the home but also charge the bank back up at a
reasonable rate, so if the loads are high and the genny only has enough to
maintain that load then what about the batteries plus I only use 75% of the
genny rating for optimum or improved duty cycle. This is only me and I am
sure every shop has there own math. 

Jerry 

 

On Wed, Apr 8, 2015 at 11:23 AM, Dana <dana at solarwork.com> wrote:

Hey All - 

 

I just got off of a phone call with my Onan generator supplier. Last
conversation with Kohler was the same story basically.

 

I was informed that their smallest water cooled generator, the RS22 (22 KW)
is now no longer "rated "for off grid. They actually called me to confirm
that this generator was for backup power to a utility inter connected house.
Tier 4 generators in the EPA CFR 40 is the Federal code what covers this, &
you are allowed 100 hours of run time for standby power and maintenance per
year. 

Q - Why am I using ridiculous sized generators for something that an 82-8300
watt generator does just fine?

A - The EPA current requirements, a shrinking economy, & manufacturers that
have to meet very expensive air quality compliance. 

The Penalty - If you get caught running a "standby power only" generator the
fine is now $39,000 per day! 

Now I am far from a polluting kind of individual and all for air quality but
this is getting the best of us. The 13KW air cooled generators are only good
for 2000 hours, & the water cooled go 20 years of moderate usage but cost a
boat load. I hate having the "Generator" talk with a new client they look at
me like I am crazy. So the air cooled units are basically throwaways and the
22KW units are way more than we need and what a client needs to spend money
on, unless you are at 10,000 ft el.

 

If you figure 30 amps/120 VAC input per inverter +/- x 2 = 7.2KW plus say
10-15% fudge or elevation factors would require an 8200-8300 watt generator.
Air cooled at 3600 RPM = 80 MPH & 1800 RPM = 40 MPH.  Even if the generator
were a bit smaller, ran slow (1200-1800 rpm) and ran a bit longer that would
be acceptable. 

So, why are we installing even 13KW air cooled or 22 KW water generators?

There is a business opportunity here folks.

 

What are you all installing?

Why?

Is it reliable?

Would you use it on your house?

 

Thanks for sharing all the wisdom and knowledge.

 

----------------------------------------------------------------------------

Dana Orzel 

Great Solar Works, Inc -  NABCEP # 051112-136

E - dana at solarwork.com  - Web - solarwork.com 

O - 970.626.5253  C - 208.721.7003 - No FAX Line

"Responsible Technologies for Responsible People since 1988"  

P Please consider the environment before printing this email.

 

 


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org




 






_______________________________________________
List sponsored by Redwood Alliance
 
List Address: RE-wrenches at lists.re-wrenches.org
 
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
 
Check out or update participant bios:
www.members.re-wrenches.org
 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150409/21639d5e/attachment-0002.html>


More information about the RE-wrenches mailing list