[RE-wrenches] Outback AGS & eq
william at millersolar.com
william at millersolar.com
Thu Feb 12 11:33:51 PST 2015
Mac:
I meant the sequence that Jay had listed:
Gen to manual on
Initiate EQ
Gen to auto
Done
William
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Mac Lewis
Sent: Thursday, February 12, 2015 10:54 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Outback AGS & eq
Hi William,
I don't see the "sequence below" that you are referencing.
Thanks
On Thu, Feb 12, 2015 at 10:47 AM, <william at millersolar.com> wrote:
Friends:
I understood the generator had to be started and stopped manually. I have a client who was using the sequence below to stop the generator automatically. To have the generator stop automatically has a convenience factor, but I do like my clients to verify the cycle has accomplished the prescribed regimen, and walking away from the process does not accomplish that.
I spoke with Outback regarding the procedure of engaging the auto mode prior to completion of the EQ and the reply was that the system had not been engineered to operate this way so the results could not be guaranteed.
William
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of jay peltz
Sent: Thursday, February 12, 2015 8:54 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Outback AGS & eq
Hi Mac
I don't think there is a global eq function.
Eq continues to be manual on inverters.
Gen to manual on
Initiate EQ
Gen to auto
Done
Jay
Peltz power.
On Feb 12, 2015, at 4:52 AM, Mac Lewis <maclewis1 at gmail.com> wrote:
Hello wrenches,
I have a question about how the global equalization function works with the Auto Gen Start on the Mate-2.
Is there a way to set up a global equalization that will ensure that the generator will shutdown after the equalization has occurred? If so, how do you set it up?
Thanks in advance
--
Mac Lewis
"Yo solo sé que no sé nada." -Sócrates
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
--
Mac Lewis
"Yo solo sé que no sé nada." -Sócrates
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150212/88d59a1a/attachment-0002.html>
More information about the RE-wrenches
mailing list