[RE-wrenches] Rapid Shut Down and the 10 Second Rule Questions

Christopher Warfel cwarfel at entech-engineering.com
Mon Feb 2 13:43:55 PST 2015


I thought it was dc only also, but PV System Conductors is not defined 
as dc, so it could be interpreted as ac and dc.

Chris
On 2/2/2015 11:14 AM, Glenn Burt wrote:
> Chris,
> I am not seeing any code reference to AC being affected by 690.12. in fact
> it seems to specifically address only DC circuits.
> In Mike Holt's new PV and the NEC book, his note recommends that the rapid
> shutdown initiator be located near the service equipment, however this is
> not addressed by the code.
>
> -Glenn Burt
>
> -----Original Message-----
> From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
> Behalf Of Christopher Warfel
> Sent: Monday, February 02, 2015 10:34 AM
> To: RE-wrenches
> Subject: [RE-wrenches] Rapid Shut Down and the 10 Second Rule Questions
>
> We have a interpretation problem among some people I work with with, and
> 690.12 Rapid Shut Down and the the 10 second time for reducing ac and dc
> conductors to 240ma, and 30V.  The word "initiation" seems to indicate that
> all affected conductors need to be at these levels within
> 10 seconds of de-energizing either the ac or dc conductors. If so, then the
> disconnects need to be co-located to meet this requirement if this
> interpretation is correct.
>
> I have read Mr. Brook's article in Solar Pro, but AHJs may feel differently.
>
> Would anyone care to weigh in on their interpretation?
>
> Thank you, Chris
>
>
>
>
>
> --
> Christopher Warfel, President
> ENTECH Engineering, Inc.
> PO Box 871, Block Island, RI 02807
> 401-466-8978
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 
Christopher Warfel, President
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
401-466-8978

-------------- next part --------------
A non-text attachment was scrubbed...
Name: cwarfel.vcf
Type: text/x-vcard
Size: 100 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150202/f1753911/attachment-0005.vcf>


More information about the RE-wrenches mailing list