Yes, beautiful. But I am still trying to figure out if it is NEC 
compliant. At first pass, it seems like it is missing a few 
disconnecting means.

On 1/3/2015 10:48 AM, Larry wrote:
> Wow, Jarmo! That is some incredible workmanship and a great way to 
> interconnect multiple inverters and chargers. You can tell they have 
> done this a few times. Thanks for sharing those photos.
> Larry Crutcher
> Starlight Solar Power Systems
> On 1/3/15 9:16 AM, Jarmo.Venalainen at schneider-electric.com wrote:
>> Hi:
>>
>> This link takes you to a site in Romania so you (likely) wont be able 
>> to read the text, but  it does have a lot of good pictures.
>>
>> This installer has been using XW since about 2007 and has a tons of 
>> experience.  I like what he does with the DC wiring/busbars.  The 
>> breakers are in the box below the inverters and charge controllers.
>>
>> http://customer.lpelectric.ro/doc/sibiu2/sibiu2_28kw_fotovoltaic.html
>>
>> JARMO
>> _____________________________________________________________________________________
>> *
>> Jarmo Venalainen*  | *Schneider Electric **  |  Solar Business*  | 
>> *CANADA*  | *Training & Development Specialist - Senior* *
>> Phone:* +604-422-2528  | *Fax:* +604-420-1591  | *Mobile:* 
>> +604-505-0291 *
>> Email:* _jarmo.venalainen at schneider-electric.com_ 
>> <mailto:jarmo.venalainen at schneider-electric.com> | 
>> *Site:*_www.SEsolar.com_ <http://www.sesolar.com/> | *Address:* 3700 
>> Gilmore Way, Burnaby, BC V5G4M1
>> _
>> _<http://%20www.sesolar.com/>
>> *** Please consider the environment before printing this e-mail
>>
>>
>>
>> From: 	drake.chamberlin at redwoodalliance.org
>> To: 	"RE-wrenches" <re-wrenches at lists.re-wrenches.org>,
>> Date: 	01/02/2015 05:18 PM
>> Subject: 	Re: [RE-wrenches] wire sizing question
>> Sent by: 	"RE-wrenches" <re-wrenches-bounces at lists.re-wrenches.org>
>>
>>
>> ------------------------------------------------------------------------
>>
>>
>>
>> 4/0 copper is good for a 24V, 4000 W inverter. What is being used for
>> multiple inverters?
>>
>> I've paralleled 4/0 into outback boxes using 2, 2" PVC conduits. It gets
>> pretty messy trying to put 4 sets of 4/0s into enclosures and battery
>> boxes (although I have worked on such systems). Does anyone have clean
>> solutions for these systems?
>>
>> Thanks,
>>
>> Drake
>>
>>
>>
>>
>>
>> > Some other things:  If you keep the conduit less than 24" long, 
>> which is
>> > recommended anyway for main battery connections, the conduit fill
>> > requirements don't apply. (see exception: 310.15(B)3a2)
>> > Using table 310.15(B)16 yeilds 230 amps for 4/0 at 75 C.  Then 240.6
>> > lists 250 amp as the next standard size of OCPD which is allowed to be
>> > used by 240.4(B)  So you can just justify 4/0.
>> > Further, many manufacturers (like Midnite) use the open air ampacity
>> > table: 310.15(B)17, since the cable is not "in conduit" and 4/0 
>> cable at
>> > 75 C is rated to 360 amps.
>> > The Free Air interpretation is not completely substantiated in the code
>> > from my read of it though.  Maybe someone more knowledgable could cite
>> > the chapter and verse that defines when the free air rating can and
>> > cannot be used.
>> > Also remember those breakers are 100% duty cycle rated, and that the
>> > inverter usually can't run any where close to 250 amps continuously.
>> > Bottomline is we've been using 4/0 with 250 amp breakers for almost 20
>> > years, and I've never seen or heard of a problem.
>> >
>> > R.Ray Walters
>> > CTO, Solarray, Inc
>> > Nabcep Certified PV Installer,
>> > Licensed Master Electrician
>> > Solar Design Engineer
>> > 303 505-8760
>> >
>> > On 1/1/2015 7:23 PM, jay peltz wrote:
>> >> Happy new year all.
>> >>
>> >> I have a question on wire sizing for the following.
>> >>
>> >> 250 amp breaker, in a UL enclosure ( say midnite or outback etc)
>> >> conduit from battery box to enclosure
>> >>
>> >> I'm wondering how folks size this for ampacity not voltage drop.
>> >>
>> >> thanks
>> >>
>> >> jay
>> >>
>> >> peltz power
>> >>
>> >>
>> >>
>> >>
>> >>
>> >> _______________________________________________
>> >> List sponsored by Redwood Alliance
>> >>
>> >> List Address: RE-wrenches at lists.re-wrenches.org
>> >>
>> >> Change listserver email address & settings:
>> >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> >>
>> >> List-Archive:
>> >> 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> >>
>> >> List rules & etiquette:
>> >> www.re-wrenches.org/etiquette.htm
>> >>
>> >> Check out or update participant bios:
>> >> www.members.re-wrenches.org
>> >>
>> >>
>> >
>> > _______________________________________________
>> > List sponsored by Redwood Alliance
>> >
>> > List Address: RE-wrenches at lists.re-wrenches.org
>> >
>> > Change listserver email address & settings:
>> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> >
>> > List-Archive:
>> > 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> >
>> > List rules & etiquette:
>> > www.re-wrenches.org/etiquette.htm
>> >
>> > Check out or update participant bios:
>> > www.members.re-wrenches.org
>> >
>> >
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>> ______________________________________________________________________
>> This email has been scanned by the Symantec Email Security.cloud service.
>> ______________________________________________________________________
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address:RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150103/178038a9/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 14092 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150103/178038a9/attachment-0002.jpe>


More information about the RE-wrenches mailing list