[RE-wrenches] 24V Zephyr Vent Fan from a Magnum MS4024PAE inverter
Ray Walters
ray at solarray.com
Wed Jan 7 12:56:57 PST 2015
The Magnums do not have relays available like the old SWs, but you can
run a Zephyr directly from either a Outback FM controller or a Midnite
Classic. Both have a controlled 200 mA, 12 output. I've had occasional
trouble running the Zephyr because as weird as this sounds: the fan can
have a start up surge that exceeds 200 mA. Its like sizing a water pump
for mice.....you still have to look at the locked rotor current and
surge current. With the Midnite Classic, it will just shut off the 12 v
output if it exceeds 200 mA, and it doesn't seem to have an error
message or warning.
You could also use a Simple Switch, or other voltage controlled
switching device (C40, Tristar, Solar Converters, etc)
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 1/7/2015 8:45 AM, Chris Daum wrote:
> Dear folks:
> Has anyone hooked up a battery vent fan, being turned on and off using
> just a Magnum MS4024PAE inverter? Is there some AUX output that can
> be used?
> Thanks as always for your help!
> Chris Daum
> Oasis Montana Inc.
> 406-777-4309
> www.oasismontana.com <http://www.oasismontana.com>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20150107/7eb4c172/attachment-0001.html>
More information about the RE-wrenches
mailing list