[RE-wrenches] Programmable Battery Charger
Brian Teitelbaum
bteitelbaum at aeesolar.com
Mon Dec 15 17:45:17 PST 2014
Larry,
I have not found a battery charger nearly as programmable as the chargers
in inverters are, and I've sold a number of inverters over the years which
were destined to be used strictly as battery chargers.
This is actually a great use for modified-square-wave inverters. The
Magnum RD2212 has a 110A charger section, and is relatively inexpensive. I
doubt that you would find a better deal, even with the added cost of the
Magnum remote unit you will need to program it. Magnum has smaller 12V
inverter/chargers too, of course.
Also a great use for old Trace SW inverters, if you can find an SW2512. I
measured the charging efficiency of an SW4024 once and came up with 72%.
Not bad at all, for a battery charger.
Brian Teitelbaum
AEE Solar
-----Original Message-----
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
Behalf Of Larry
Sent: Monday, December 15, 2014 3:04 PM
To: RE-wrenches
Subject: [RE-wrenches] Programmable Battery Charger
Wrenches,
Does anyone know of a 120/12 volt battery charger that can be programmed
for absorb and float voltage and time in absorb mode? I have been needing
this product for many years but I can only find it in inverters with built
in chargers from Magnum, Outback, and Xantrex.
--
Thank you,
Larry Crutcher
Starlight Solar Power Systems
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.htm
l
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
More information about the RE-wrenches
mailing list