[RE-wrenches] Parallel Wire combining
Bill Turberville
billturb at ece-llc.com
Tue Dec 2 10:13:28 PST 2014
The ampacity is twice the ampacity of 1-1/0 conductor under the same
conditions.
William C. Turberville P.E.
President
Electrical Contracting Enterprises LLC
3080 Stage Post Dr ste 107
Bartlett, TN 38133
901-348-9230 ext 101 phone
901-289-6346 cell
901-348-2192 FAX
*From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
Behalf Of *Larry
*Sent:* Tuesday, December 02, 2014 12:09 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Parallel Wire combining
OK, let's use 1/0 for the example. 108,350 x 3 = 325,050. Do I now have a
cable between 300 and 350 AWG?
Thank you,
Larry
On 12/2/14 10:51 AM, Bill Turberville wrote:
The minimum conductor size that can be paralleled, according to the NEC is
1/0.
William C. Turberville P.E.
President
Electrical Contracting Enterprises LLC
3080 Stage Post Dr ste 107
Bartlett, TN 38133
901-348-9230 ext 101 phone
901-289-6346 cell
901-348-2192 FAX
*From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
Behalf Of *Jerry Shafer
*Sent:* Tuesday, December 02, 2014 11:45 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Parallel Wire combining
We have installed multible mcm 500 to meet this and there were three on
each leg but that was because of the required size and bending room
Jerry
On Dec 2, 2014 7:43 AM, "Larry" <larry at starlightsolar.com> wrote:
Wrenches,
If I combine 3 conductors of equal length in parallel, is the resulting
size equal to 3 times the Circular Mil area? For example, #4 is 42,080cm so
are three #4's close to 2/0 (134,200cm) in size? Is it as simple as this?
Assuming the conductors can not be removed individually, does this mean the
current capacity is equal to the resulting wire size?
Thanks, Larry
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20141202/a72e73fb/attachment-0002.html>
More information about the RE-wrenches
mailing list