[RE-wrenches] Suspect MX 60
Jarmo.Venalainen at schneider-electric.com
Jarmo.Venalainen at schneider-electric.com
Tue Nov 18 10:03:11 PST 2014
Hi:
This may not be the problem, but I wanted to bring it up as I have heard
of a few cases of battery boiling issues with various charge controllers
and want to suggest a possible cause.
I'll do this point form. It's easier to describe it that way:
1. Solar charge controllers are programmed to go to bulk charge in the
morning.
2. The intensity of the sunlight starts off low in the morning and
depending on the weather during the day, the intensity can reach any level
between virtually 0% and 100%.
3. The exit criteria for bulk is that the battery voltage reaches the
Vbulk/abs volts setting or a bulk/abs timer times out.
4. If the sunlight conditions are just right to keep the charging voltage
just below the Vbulk/abs setpoint, the exit from bulk/abs will be the
timer.
5. Bulk/Abs timers are usually set for rather a long time, many hours is
not uncommon.
6. Given the above, it is possible that the battery stays at gassing
voltages for many hours every day at certain times of the year when the
sunlight intensity is just right to support that.
7. As a consequence the boiling problem will show up only at particular
sites, particular battery/charge controller sizes and particular times of
year.
Again, I am not suggesting that this is necessarily the cause of battery
"boiling" in systems with solar charge controllers, but it could be a
reason.
2nd ps. All manufacturers do precise battery voltage/current measurements
on the bench with a wide variety of conditions, but we will never be able
to simulate the 1000's of conditions that happen on the 1000's of installs
out there. With that in mind, on-site battery voltage/current data
logging is a very powerful tool when investigating these kinds of issues.
JARMO
_____________________________________________________________________________________
Jarmo Venalainen | Schneider Electric | Solar Business | CANADA |
Training & Development Specialist - Senior
Phone: +604-422-2528 | Fax: +604-420-1591 | Mobile: +604-505-0291
Email: jarmo.venalainen at schneider-electric.com | Site: www.SEsolar.com
| Address: 3700 Gilmore Way, Burnaby, BC V5G4M1
*** Please consider the environment before printing this e-mail
From:
Drake <drake.chamberlin at redwoodalliance.org>
To:
RE-wrenches <re-wrenches at lists.re-wrenches.org>,
Date:
11/18/2014 09:15 AM
Subject:
[RE-wrenches] Suspect MX 60
Sent by:
"RE-wrenches" <re-wrenches-bounces at lists.re-wrenches.org>
Hello Wrenches,
An MX 60 boiled a 24 volt bank of 4 Trojan L-16 batteries last summer. The
batteries all checked out to be in good shape. It is not totally clear
that the CC was not set to auto equalize, but the EQ voltage was only set
at 31.0 V.
The battery bank has been replaced by 8 Full River L-16 AGM batteries. The
parameters have all been reset for AGM with EQ disabled. The homeowners
are concerned that the charge control may not work, and damage their new
battery bank.
If there is a problem with the CC, it is very intermittent. Has anyone
ever seen an intermittent MX 60?
Outback tech support says if we send it in they will update the firmware
for $90, and do a 24 hour bench test. It appears that the firmware update
will not do anything useful for this off grid system. There are no new
boards available for this unit. I'm not sure if the bench test will show
up an intermittent problem.
Has anyone had this situation before? Would it be better to:
Replace the CC
Send the CC to Outback
Do nothing
Thank you,
Drake
Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV
740-448-7328
http://athens-electric.com/
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20141118/3a9cb4bd/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 14092 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20141118/3a9cb4bd/attachment-0002.jpe>
More information about the RE-wrenches
mailing list