[RE-wrenches] Passive Battery Venting
RE Ellison
reellison at gmail.com
Thu Oct 30 05:12:20 PDT 2014
To do it totally passive you will need a long (tall) pipe up the side of the
building, probably painted a dark color to have the sun help warm the tube
to help encourage it to vent up, not draw into the building. Put a 180 on
the top to keep the rain out and a screen to keep out the bugs.
With outside venting the batteries will just draw in room temperature air,
if the room is 70 the battery min temp will be 70. If they are in a basement
they will naturally draw in outside air, run the vent as high as you can to
help prevent that. If you are using a Classic use the relay to turn the fan
on and off at a specific battery voltage. Use a brushless fan and a voltage
powered relay if no other choice. Do not put the relay in the battery box!
Sealed batteries do need to be vented. I have seen them gas when things go
wrong, not pleasant.
I wouldn't do it without a fan for LA batteries but it would work for
sealed. If the home has a makeup air system or huge exhaust system all bets
are off.
Just some thoughts,
Bob Ellison
-----Original Message-----
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
Behalf Of Drake
Sent: Wednesday, October 29, 2014 8:19 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Passive Battery Venting
Hi Daniel,
I typically vent them the way you do, which will allow any small amount of
hydrogen out. The customer is absolutely adamant about venting these to the
outside. I will cooperate so long as his method doesn't compromise the
system through cooling the batteries unnecessarily in the dead of winter.
He is a lawyer and came to the conclusion of the need for venting to the
outside from reading the NEC which says that sealed batteries "require the
same amount of ventilation" as liquid lead acid batteries. The code also
says to vent appropriate to battery technology, so the code says two
conflicting things. On the other hand, it doesn't say that liquid
electrolyte batteries need to be vented to the outside. They will sure stink
if you vent them to the inside.
Drake
At 09:54 AM 10/29/2014, you wrote:
>I just re-read the original post Drake. These are AGM batteries. Do you
have
>a "belt, suspenders,...then a rocket pack" type of client here?
>
>We typically vent our AGM boxes with small louver vents top and bottom to
>allow the batteries to ventilate for cooling purposes, not H2 concerns.
>
>With Regards,
>
>Daniel Young,
>NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90
>NABCEP Certified Solar Heating InstallerTM: Cert #SH031409-13
>
>-----Original Message-----
>From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
>Behalf Of Ray Walters
>Sent: Tuesday, October 28, 2014 11:12 PM
>To: RE-wrenches
>Subject: Re: [RE-wrenches] Passive Battery Venting
>
>That's why we usually have the batteries in a garage, basement, or out
>building that is not open to the living space.
>I've seen some cases of very well sealed and insulated enclosures allowing
>batteries to over heat, and also build up a lot of acid damaged
connections.
>Boxes I've seen with more air space and less sealing don't get this build
>up, but you're correct: they do occasionally allow H2S into the surrounding
>area.
>
>R.Ray Walters
>CTO, Solarray, Inc
>Nabcep Certified PV Installer,
>Licensed Master Electrician
>Solar Design Engineer
>303 505-8760
>
>On 10/28/2014 8:10 PM, Jerry Shafer wrote:
> >
> > We do what we can to seal the enclosure so if or when a battery fails
> > and really gasses off the two vents on the same wall regardless of
> > wind direction will vent the gas. If it is not sealed then the gas can
> > travel through out the area this is not advised.
> >
> >
>
>_______________________________________________
>List sponsored by Redwood Alliance
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change listserver email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out or update participant bios:
>www.members.re-wrenches.org
>
>
>
>-----
>No virus found in this message.
>Checked by AVG - www.avg.com
>Version: 2012.0.2247 / Virus Database: 4031/7973 - Release Date: 10/29/14
>
>-----
>No virus found in this message.
>Checked by AVG - www.avg.com
>Version: 2012.0.2247 / Virus Database: 4031/7973 - Release Date: 10/29/14
>
>_______________________________________________
>List sponsored by Redwood Alliance
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change listserver email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out or update participant bios:
>www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
More information about the RE-wrenches
mailing list