Admittedly I only partially understand your scenario, but I have found that
multiple points of interconnection to a single service are not problematic
as long as the rules of 690.64 (NEC 2008) are followed. We have done supply
side and load side connections on the same service - which sometimes
happens if we are adding onto a PV system where there is already a max'd
out load side connection.
Jason Szumlanski
On Wed, Oct 22, 2014 at 9:15 AM, Allen Frishman <amfrish at aeonsolar.com>
wrote:
> Wrenchers,
> I am working on a multi building complex that is part of a isolated grid
> (multiple buildings are fed from one central building). All of the power
> from the utility enters one central building via a 4000AS/4000AF Service
> Switch. The 4000A Service switch feeds a 3 section cabinet with (5) fused
> switches per section. The fused switches in each of these sections then
> feed a different building in the complex. My plan is to install a solar
> array with inverters on each of these buildings and grid connect to the
> conductors at the individual building entrances. The majority if not all
> of the solar power will feed directly into the building that the array is
> located on however since the point of solar grid connection is to the
> conductors feeding the building that originate in the central buildings
> switch gear I am trying to get my head around the need to comply with the
> opposite side of the bus rule in the 3 sections located in the central
> building.
>
> I am hoping I am missing a rule in the NEC that will allow the multiple
> grid connections described to connect to all of the fused switch positions
> in the central buildings switch gear.
>
> All feedback is appreciated.
>
> *Al Frishman*
> AeonSolar
>
> *(917) 699-6641 <%28917%29%20699-6641> - cell*
> *(888) 460-2867 <%28888%29%20460-2867>*
> *www.aeonsolar.com <http://www.aeonsolar.com/>*
>
>
>