[RE-wrenches] TL inverter with long DC Feeder
Isaac Opalinsky
David.Opalinsky at sunpower.com
Tue Oct 7 13:06:31 PDT 2014
William,
What is your string configuration? The SMA TL inverters have a very low operating voltage window, going down to 125 Vdc, but you still have the issue of the disconnect.
[cid:image001.png at 01CFE248.3F9A1920]
Have you looked at ABB’s (PowerOne) TL inverters: http://www.abb.us/product/us/9AAC179447.aspx?country=US? They can be programmed to operate down to 90 Vdc, and they give you the ability to combine upstream and have the 2 MPPT’s operate as one, allowing you to combine outside of the inverter and bring a single set of PV output conductors to the inverter’s DC disconnect:
Isaac Opalinsky | Technical Trainer | SunPower Corporation
Desk 443-569-3476 | Cell 443-277-6286
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of William Miller
Sent: Tuesday, October 07, 2014 12:01 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] TL inverter with long DC Feeder
Friends:
If only an SMA would work here. But DC volts too low. We are using Solectria PVI5200TLS.
We do not use PV wire. We transition to THWN-2 in conduit immediately.
William
Miller Solar
On Oct 6, 2014, at 8:30 PM, Chris Mason <cometenergysystems at gmail.com<mailto:cometenergysystems at gmail.com>> wrote:
I presumed SMA TL series.
On Mon, Oct 6, 2014 at 10:02 PM, Jerry Shafer <jerrysgarage01 at gmail.com<mailto:jerrysgarage01 at gmail.com>> wrote:
As i read the thread you say TL which TL SMA, AE ect. They have defferent dc input designs
On Oct 6, 2014 12:21 PM, "jay peltz" <jay at asis.com<mailto:jay at asis.com>> wrote:
I do believe the outback and midnite combiners have a lock hole to prevent exactly your concern.
unauthorized access.
jay
peltz power
On Oct 6, 2014, at 11:40 AM, William Miller wrote:
Wrenches:
We are getting up to speed on using transformer-less inverters. I have advocated long for the additional safety offered by these inverters but I am realizing the trade-offs with the new technology: The implementation gets more complicated with the requirement for PV wire, OCPD and disconnecting means for plus and minus and plus providing Arc Flash rated equipment.
I am currently designing a system that will locate the PV about 400 feet from the residence. The system will utilize 2 Solectria 5200 watt inverters at the residence. I would like to provide disconnecting means for the 4 strings at the array, in case of any needed service or excavating. Preferably I’d like the disconnecting means to be deployable by a lay person (i.e. the gardener).
Finding an 8 pole, arc flash, 600 VDC rated disconnect is not easy. I could install an Outback 8 circuit combiner with 8 touch-safe fuse holders. The new combiners have had dead-fronts for a while now. The gardener needs only to have a Philips screw driver to open this cover. Any better ideas out there?
Thanks,
William
<image002.jpg>
Lic 773985
millersolar.com<http://www.millersolar.com/>
805-438-5600<tel:805-438-5600>
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
--
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician
www.cometsolar.com<http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20141007/c3059d5d/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 20910 bytes
Desc: image001.png
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20141007/c3059d5d/attachment-0005.png>
More information about the RE-wrenches
mailing list