If you have access to the attic, then one option is to reroute the plumbing
vent to a north facing roof or an unused section of the roof.  I've done
this in the past.

On Thu, Sep 25, 2014 at 5:40 PM, Benn Kilburn <benn at skyfireenergy.com>
wrote:

> I'll echo what Matt suggests about not relying on an inspector (electrical
> or plumbing) to "catch" this.
>
> That doesn't make it a best practice and just because you can get away
> with it then you should be doing it.
> Do your due diligence and find out what the Plumbing Code in your area
> requires AND run the idea/concept by an inspector (plumbing).
> And again, just because the plumbing code may allow it, technically, it
> still doesn't make it a best practice method.
>
> I had a plumbing inspector get back to me today and he cited a plumbing
> code 2.5.6.5 Article 5 (Alberta Plumbing Code, I assume), which basically
> says the sewer vent must be high enough to prevent any run-off from
> entering the vent *however it cannot be less than 150mm (6 inches)*.
> This means we could not install mods over a sewer vent using our typical
> racking system (on asphalt shingles) which only gets the back of the module
> 4 to maybe 4-1/2" off the roof.  And if we did install a taller L-foot or
> stand-off that would give us say an inch or even 3 inches of clearance,
> then you have the potential issue of condensation freezing and building up
> on the back of the module in the winter and potentially blocking the vent
> altogether.
> That might not be a concern if you are in a warmer climate, but here in
> Alberta and i'm sure much of the US, it is very possible that this could
> happen.
>
> Regardless, i'm pleased to have found out the minimum height required for
> these vents as i will be looking to trim down any taller ones that will
> cause some shading.  Always looking to maximize system performance, a few
> inches (several in some cases) trimmed off the height of a vent will be
> just that much less shading and increased system output. I can't imagine it
> would be too much, but....
>
> Cheers,
> Benn
>
> On Thu, Sep 25, 2014 at 6:22 AM, Matt Partymiller <
> matt at solar-energy-solutions.com> wrote:
>
>> Carl,
>>
>> In our shared region plumbing code requires vents be 12" above roof line.
>> Electrical inspectors probably won't catch this, plumbing inspectors
>> probably won't get on a roof, but still there is a code concern.  You
>> might exercise some caution.
>>
>> Matt
>>
>>
>> Matthew Partymiller
>> Solar Energy Solutions LLC
>> (877) 312-7456
>> matt at solar-energy-solutions.com
>>
>> On Wed, September 24, 2014 6:49 pm, Carl Adams wrote:
>> > Bruce,
>> > We routinely cut off DWV as suggested by earlier posts so that they are
>> at
>> > least 1 inch below the surface of the back of the module.
>> >
>> > To be clear these are sewage intake air vents and not exhaust vents for
>> > heating appliances.
>> >
>> > We do place a quarter inch wire cloth over the cut off vent and apply a
>> > four inch stainless steel hose clamp around the pipe just to prevent
>> > foreign objects from entering the vent pipe.
>> >
>> > I have never had an inspector question this method.
>> >
>> >
>> > With Regards
>> > Carl Adams, President
>> > SunRock Solar
>> > 513.290.9072 (cell)
>> > 513.766.6025 (office)
>> >
>> >
>> > On Sep 24, 2014, at 1:37 PM, Ray Walters <ray at solarray.com> wrote:
>> >
>> >
>> > I agree with Kurt: you need a licensed       plumber in your area to
>> > advise you, if you're trying to keep the AHJs happy . 2nd,  I'm very
>> sure
>> > you don't want an exhaust/ combustion type vent under the array.  I've
>> > had several over the years, and seen some arrays installed over them.
>> > They can get fairly hot and put quite a bit of steam out.  I would not
>> > trust the module backing material to a concentrated long term dose;
>> which
>> > module is going to have a problem first? R.Ray Walters
>> > CTO, Solarray, Inc
>> > Nabcep Certified PV Installer,
>> > Licensed Master Electrician
>> > Solar Design Engineer
>> > 303 505-8760
>> > On 9/24/2014 11:16 AM, Kurt Johnsen wrote:
>> >
>> >> Should you decide to lower your plumbing vents I have found an inside
>> >> pipe cutter to be an inexpensive and handy tool. Cut the vent and lead
>> >> off an inch above your desired pipe height and use the inside cutter to
>> >> cut the pvc pipe. Go slow and be careful to keep air space between the
>> >> pvc and lead as the lead will cut very easily.
>> >>
>> >>
>> >>
>> >> Also I wouldn't rely on us well intentioned wrenches to make the call
>> >> on the plumbing code in your jurisdiction. Though the state plumbing
>> >> codes are usually based on the international code, there will be
>> >> differences. If you can't pull up your state plumbing code online then
>> >> ask your plumbing inspector. In Florida the minimum height above a roof
>> >> surface is 6" (904.1). As for relocating 905.2 states that “all vent
>> >> and branch vent pipes shall be so graded and connected as to drain back
>> >> to the drainage pipe by gravity†. Table 710.1(1) shows that for
>> >> 1.5† pipe a slope of ¼† per foot is sufficient to handle 3
>> >> fixtures. I would take that to indicate ¼† / foot is plenty for a
>> >> 1.5† vent.
>> >>
>> >>
>> >>
>> >>> On Wed, Sep 24, 2014 at 11:20 AM, Dave Click <daveclick at fsec.ucf.edu>
>> >>> wrote:
>> >>> Flipping through the '04 plumbing code I see a few slopes called out
>> >>> (1/4" per 1' for fixture vents, 1" per 1' for circuit vents, 1/2" per
>> >>> 1' for combination drain/vent...). Fixture vents have a maximum
>> >>> distance of a few feet from fixture trap to vent, but I don't think
>> >>> this prevents you from then running that vent horizontally. 916.2
>> >>> states that for vents other than stack vents or vent stacks if your
>> >>> vent is >40' you need to upsize the whole vent pipe (tough to do for
>> >>> an existing building, of course). Stack vents have a "maximum
>> >>> developed length" of 100' for a 1.5" vent which should be enough
>> >>> space to get away from under the PV. I don't see any slope
>> >>> requirements specifically for stack vents but my non-plumber's eye
>> >>> may be missing something.
>> >>>
>> >>> The stack vent sizing Table 916.1 appears (in part) here too and it
>> >>> looks like the tables match up to a 2.5":
>> >>> http://www.engineeringtoolbox.com/drainage-vents-d_1110.html
>> >>>
>> >>>
>> >>> DKC
>> >>>
>> >>>
>> >>>
>> >>>
>> >>>
>> >>> On 2014/9/24 10:19, Jason Szumlanski wrote:
>> >>>
>> >>>> I am unable to find anything in the Florida code that precludes
>> >>>> covering a plumbing vent. The code does require the vent to be 6"
>> >>>> above the roof surface I believe.
>> >>>>
>> >>>> I was unable to determine if these vents need to be vertical with
>> >>>> no bends in the attic. Obviously you wouldn't want to create a trap
>> >>>> in the attic, but a couple of 45's to relocate a plumbing vent to
>> >>>> accommodate more PV seems like a desirable thing to do sometimes.
>> >>>> Does anyone know if these can be relocated, i.e. to an adjacent
>> >>>> roof surface?
>> >>>>
>> >>>> On my own home I had a vent to deal with. I broke out my saws-all,
>> >>>> split the lead like a banana and peeled it back, cut the pipe at an
>> >>>> angle, and folded the lead back into the pipe after applying
>> >>>> sealant between the lead and pipe. There is a 1" gap between the
>> >>>> rim of the pipe and the back of the module. My theory on this
>> >>>> working safely is that, a) there will be far less rainwater falling
>> >>>> in and around this pipe with a module over it, and b) it is about
>> >>>> 24" from the roof ridge and there is a module over it so there will
>> >>>> be very little water sheeting                           down from
>> >>>> above the vent. Code notwithstanding, I felt this was a solid
>> >>>> method on my own home, and I have inspected it after 6 months of
>> >>>> Florida downpours and found no issues.
>> >>>>
>> >>>>
>> >>>>
>> >>>> Jason Szumlanski
>> >>>> Fafco Solar
>> >>>>
>> >>>>
>> >>>>
>> >>>> On Wed, Sep 24, 2014 at 6:38 AM, Bill Loesch
>> >>>> <solar1online at charter.net> wrote:
>> >>>>
>> >>>>>
>> >>>>> Bruce, August, et al,
>> >>>>>
>> >>>>>
>> >>>>> This is but one more example of confusing terminology. A plumbing
>> >>>>> vent is not an exhaust vent!
>> >>>>>
>> >>>>> A plumbing vent (what August calls a cold vent) is provided to
>> >>>>> allow the sanitary drain traps (and perhaps more) to operate
>> >>>>> properly. Without the properly functioning traps you would have
>> >>>>> sewer gas smell and sewer gas from the plumbing fixtures. This
>> >>>>> was commonplace when indoor plumbing was introduced to early
>> >>>>> adopters.
>> >>>>>
>> >>>>> An exhaust vent is another animal entirely. An exhaust vent
>> >>>>> carries the combustion products to a suitable exterior location
>> >>>>> for dilution with ambient air. With the advent of power vented
>> >>>>> combustion appliances, a direct vent (one that takes in
>> >>>>> combustion air from the outside and naturally exhausts combustion
>> >>>>> products to the outside) is IMHO the only responsible way to
>> >>>>> install any power vented appliance in a freezing climate. (Power
>> >>>>> vented appliances come in both condensing and non-condensing
>> >>>>> flavors-they can penetrate the side wall or the roof).
>> >>>>> Originally, two separate pipes (with two independent properly
>> >>>>> separated penetrations) was used. That technique is still often
>> >>>>> used today. More recently concentric vents have been introduced
>> >>>>> both for condensing and non-condensing applications. A concentric
>> >>>>> vent can simplify some installations by putting the exhaust pipe
>> >>>>> inside a larger air intake pipe allowing for one, albeit larger,
>> >>>>> penetration. As you might imagine if the exhaust flow is
>> >>>>> hindered/diverted/redirected by an inappropriately located solar
>> >>>>> module combustion gasses will be re-ingested into the intake air.
>> >>>>> Not good for equipment performance. My understanding is the power
>> >>>>> vented appliance manufacturer dictates what kind of
>> >>>>> separation/clearances are needed with their product. My guess is
>> >>>>> you find they want at least a foot of separation between the top
>> >>>>> of the " inverted cone" and the module. Probably not what you had
>> >>>>> in mind for an aesthetically pleasing installation.
>> >>>>>
>> >>>>> I hope this helps,
>> >>>>> Bill Loesch
>> >>>>> Solar 1 - Saint Louis Solar
>> >>>>> 314 631 1094
>> >>>>> On 23-Sep-14 6:54 PM, August
>> >>>>> Goers wrote:
>> >>>>>
>> >>>>>> Bruce and All,
>> >>>>>>
>> >>>>>>
>> >>>>>> Sorry, I hit send before I had a chance to complete my
>> >>>>>> thoughts. What I meant to say was that I've found AHJs often
>> >>>>>> allow us to cover cold plumbing vents but I've never tried or
>> >>>>>> had any luck with covering hot vents including condensing boiler
>> >>>>>> PVC vents. Once again, if in doubt you
>> >>>>>> could see what the plan checker or inspector thinks.
>> >>>>>>
>> >>>>>> Best,
>> >>>>>>
>> >>>>>>
>> >>>>>> August
>> >>>>>>
>> >>>>>>
>> >>>>>> -----Original Message-----
>> >>>>>> From: August Goers [mailto:august at luminalt.com]
>> >>>>>> Sent: Tuesday, September 23, 2014 4:15 PM
>> >>>>>> To: 'RE-wrenches'
>> >>>>>> Subject: RE: [RE-wrenches] Modules over vents
>> >>>>>>
>> >>>>>>
>> >>>>>> Bruce,
>> >>>>>>
>> >>>>>>
>> >>>>>> I'll send you the CA plumbing code vent section offlist
>> >>>>>> (attachment too
>> >>>>>> large for this list). The way I read the code is that you
>> >>>>>> technically can't cover any type of plumbing or hot vent.
>> >>>>>> However, and I've run into
>> >>>>>> little resistance from AHJs in the Bay Area by covering these.
>> >>>>>> You might
>> >>>>>> want to check in with your plan checker.
>> >>>>>>
>> >>>>>> Best,
>> >>>>>>
>> >>>>>>
>> >>>>>> August
>> >>>>>>
>> >>>>>>
>> >>>>>> Luminalt
>> >>>>>>
>> >>>>>>
>> >>>>>> -----Original Message-----
>> >>>>>> From: RE-wrenches
>> >>>>>> [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
>> >>>>>> Behalf Of Bruce Leininger
>> >>>>>> Sent: Tuesday, September 23, 2014 3:49 PM
>> >>>>>> To: RE-wrenches
>> >>>>>> Subject: [RE-wrenches] Modules over vents
>> >>>>>>
>> >>>>>>
>> >>>>>> Hi all.  We're designing a system on a roof that is literally
>> >>>>>> infested with plumbing, exhaust and combustion vents.  The
>> >>>>>> combustion vents are PVC and none of the vents are more than
>> >>>>>> 1.5' above the roof.
>> >>>>>>
>> >>>>>>
>> >>>>>> A racking company says that we can cover them with modules,
>> >>>>>> since the modules will be at least 4' above the roof.  They have
>> >>>>>> not yet provided any building code references to say that this
>> >>>>>> is ok.  Do any of you know if the building code allows this?
>> >>>>>>
>> >>>>>> Thanks.
>> >>>>>>
>> >>>>>>
>> >>>>>> Bruce
>> >>>>>>
>> >>>>
>> >>>>
>> >>>>
>> >>>> _______________________________________________
>> >>>> List sponsored by Redwood Alliance
>> >>>>
>> >>>>
>> >>>> List Address: RE-wrenches at lists.re-wrenches.org
>> >>>>
>> >>>>
>> >>>> Change listserver email address & settings:
>> >>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> >>>>
>> >>>>
>> >>>> List-Archive:
>> >>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maill
>> >>>> ist.html
>> >>>>
>> >>>> List rules & etiquette:
>> >>>> www.re-wrenches.org/etiquette.htm
>> >>>>
>> >>>> Check out or update participant bios:
>> >>>> www.members.re-wrenches.org
>> >>>
>> >>>
>> >>> _______________________________________________
>> >>> List sponsored by Redwood Alliance
>> >>>
>> >>>
>> >>> List Address: RE-wrenches at lists.re-wrenches.org
>> >>>
>> >>>
>> >>> Change listserver email address & settings:
>> >>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> >>>
>> >>>
>> >>> List-Archive:
>> >>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillis
>> >>> t.html
>> >>>
>> >>> List rules & etiquette:
>> >>> www.re-wrenches.org/etiquette.htm
>> >>>
>> >>> Check out or update participant bios:
>> >>> www.members.re-wrenches.org
>> >>
>> >>
>> >>
>> >> _______________________________________________
>> >> List sponsored by Redwood Alliance
>> >>
>> >>
>> >> List Address: RE-wrenches at lists.re-wrenches.org
>> >>
>> >>
>> >> Change listserver email address & settings:
>> >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> >>
>> >>
>> >> List-Archive:
>> >> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist
>> .
>> >> html
>> >>
>> >> List rules & etiquette:
>> >> www.re-wrenches.org/etiquette.htm
>> >>
>> >> Check out or update participant bios:
>> >> www.members.re-wrenches.org
>> >>
>> >
>> > _______________________________________________
>> > List sponsored by Redwood Alliance
>> >
>> >
>> > List Address: RE-wrenches at lists.re-wrenches.org
>> >
>> >
>> > Change listserver email address & settings:
>> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> >
>> >
>> > List-Archive:
>> >
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.ht
>> > ml
>> >
>> > List rules & etiquette:
>> > www.re-wrenches.org/etiquette.htm
>> >
>> > Check out or update participant bios:
>> > www.members.re-wrenches.org
>> >
>> > _______________________________________________
>> > List sponsored by Redwood Alliance
>> >
>> >
>> > List Address: RE-wrenches at lists.re-wrenches.org
>> >
>> >
>> > Change listserver email address & settings:
>> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> >
>> >
>> > List-Archive:
>> >
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.ht
>> > ml
>> >
>> > List rules & etiquette:
>> > www.re-wrenches.org/etiquette.htm
>> >
>> > Check out or update participant bios:
>> > www.members.re-wrenches.org
>> >
>> >
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>
>
> --
>
> *Benn Kilburn *
> CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Energy Inc
> 6706 – 82 Ave NW | Edmonton, AB | T6B 0E7
> P: 780-474-8992 | F: 888-405-5843 | www.skyfireenergy.com
> [image: email] <benn at skyfireenergy.com> [image: facebook]
> <https://www.facebook.com/SkyFireEnergy> [image: twitter]
> <https://twitter.com/SkyFireEnergy> [image: linkedin]
> <https://www.linkedin.com/company/283735?trk=tyah&trkInfo=tarId%3A1408655033432%2Ctas%3Askyfire%2Cidx%3A2-2-5>
>  [image: google] <https://plus.google.com/+SkyFireEnergy/>
>
> [image: SkyFire Energy Logo_horizontal]
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>


-- 

Cordially,

*Nick Soleil*


*Field Applications Engineer*

*Enphase Energy*

Mobile: (707) 321-2937

*The Enphase System** | *Empowering You in 2014
<http://www.enphase.com/?utm_source=emailsignature&utm_medium=release&utm_campaign=Jan14>


 1420 North McDowell

Petaluma, CA 94954

www.enphase.com <http://www.enphaseenergy.com/>

P: (707) 763-4784 x7267

F: (707) 763-0784

E: nsoleil at enphaseenergy.com


NABCEP Certified Solar PV Installer #03262011-300

California C10 Licensed Electrician #986315

Texas Master Electrician #284451

<nsoleil at enphaseenergy.com>

“Don’t get me wrong: I love nuclear energy! It’s just that I prefer fusion
to fission. And it just so happens that there’s an enormous fusion reactor
safely banked a few million miles from us. It delivers more than we could
ever use in just about 8 minutes. And it’s wireless!”

- William McDonough



This email message is for the sole use of the intended recipient(s) and may contain confidential and/or privileged information. If you are not an intended recipient, you may not review, use, copy, disclose or distribute this message. If you received this message in error, please contact the sender by reply email and destroy all copies of the original message. 