[RE-wrenches] LiFePo4
Mac Lewis
maclewis1 at gmail.com
Tue Sep 16 05:44:50 PDT 2014
Hello wrenches,
How do you get PV power into the battery management system? Are there PV
application specific battery management systems, or are these AC loads?
Thanks
On Tue, Sep 16, 2014 at 12:31 AM, William Miller <william at millersolar.com>
wrote:
> Friends:
>
>
>
> Here are the specific batteries I am looking at:
>
>
>
> William
>
>
>
>
>
> [image: Gradient Cap_mini]
> Lic 773985
> millersolar.com <http://www.millersolar.com/>
> 805-438-5600
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
> Behalf Of *Jarmo.Venalainen at schneider-electric.com
> *Sent:* Monday, September 15, 2014 7:09 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] LiFePo4
>
>
>
> Hi:
>
> We've done some testing and operation of Lion battery banks in the 10 kWh
> range with our inverter chargers and so far the most important findings are:
>
> 1. The battery pack must have its own battery management system to:
> a. regulate the individual cell voltages during charge and discharge
> b. balance the cell voltages during charge and discharge
> c. adjust cell charging voltages due to temperature variations
> d. not provide a continuous float voltage to the battery bank
> d. provide a built in safety cutoff disconnect, which turns off the
> current if for any reason either the charge or discharge current is too
> high.
>
> A series string of Lion cells, without the battery management system
> functions above is very likely to result in damaged cells or worse. The
> most likely mechanism which ultimately causes damage is individual cell
> temperature or cell to cell voltage imbalance.
>
> 2. The inverter system must be designed so that the inverter never draws
> so much current that the current limit circuit in the battery bank is
> triggered.
>
> 3. It may be necessary to adjust the current limit circuit as they
> typically respond within milli-seconds and may be triggered on simple power
> up as the inverter cap bank charges up.
>
> 4. When working with Lion, the inverter/charger should be configured so
> that it is a simple current limited voltage source when in charge mode.
> The built in battery management system should take care of the required
> charge cycle operation.
>
> 5. Whether the pack is LiFePO4, Lion polymer or other does not appear to
> be as important as a having a reputable brand and more importantly a well
> designed built in battery management system.
>
> The short version is that lead acid cells are amazingly forgiving with
> regards charging and discharging voltages, currents and temperatures. Lion
> cells on the other hand are amazingly sensitive and going out of bounds on
> any of these can and will cause irreparable damage.
>
> Given the sensitivity, it doesn't make sense to take on responsibility for
> Lion battery management.
>
> Management of that sensitivity and responsibility is best left to the
> battery bank manufacturer.
>
> JARMO
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
--
Mac Lewis
*"Yo solo sé que no sé nada." -Sócrates*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140916/d843eb65/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1460 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140916/d843eb65/attachment-0005.jpg>
More information about the RE-wrenches
mailing list