[RE-wrenches] Inverters Maximum Input Ratings

Will White William.White at rgsenergy.com
Tue Aug 26 08:46:12 PDT 2014


In my opinion in regards to that SolarWorld recall even though they had the wrong lay in lug part specified in their manual (not tinned).  Any installer worth his salt knows that you don’t put copper and aluminum together so shame on any installer who put untinned lugs on a module, SolarWorld or otherwise.

Thanks,
Will

Will White
Operations Manager - New England
RGS Energy


64 Main St. |Montpelier, VT 05602
tel 802.223.7804 | mobile 802.234.3167 | fax 802.223.8980

RGSEnergy.com<http://www.rgsenergy.com/> | william.white at rgsenergy.com<mailto:william.white at rgsenergy.com>

Confidentiality Note: This e-mail message may contain confidential or legally privileged information and is intended only for the use of the intended recipient(s). Any unauthorized disclosure, dissemination, distribution, copying or the taking of any action in reliance on the information herein is prohibited. E-mails are not secure and cannot be guaranteed to be error free as they can be intercepted, amended, or contain viruses. Anyone who communicates with us by e-mail is deemed to have accepted these risks. RGS Energy is not responsible for errors or omissions in this message and denies any responsibility for any damage arising from the use of e-mail. Any opinion and other statement contained in this message and any attachment are solely those of the author and do not necessarily represent those of the company.






From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Marco Mangelsdorf
Sent: Tuesday, August 26, 2014 2:11 AM
To: 'RE-wrenches'
Subject: [RE-wrenches] Inverters Maximum Input Ratings

Look, guys, what’s beyond dispute is that when we size the solar array higher than the nameplate inverter output, there will be clipping that takes place….i.e., harvestable solar power that goes nowhere.  The higher that oversize percentage, the more clipping will take place.

If the design choice, as noted below, is to use a 270-watt module (from a manufacturer that learned last week that a recall notice was published by the U.S. Consumer Product Safety Commission https://www.cpsc.gov/en/Recalls/2014/SolarWorld-Recalls-Solar-Systems-with-Copper-Grounding-Lugs/ ), does it make sense to use a micro inverter that has a max output of about 225 watts (M215) or 250 watts (M250) when there are micros (e.g., ABB 300) that can handle the full output of the 270 which guarantees NO clipping?

marco

From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jerry Shafer
Sent: Monday, August 25, 2014 8:00 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Inverters Maximum Input Ratings


Why dont you use the m250 anyway as the 250's so far are more reliable then the 215 have been. A little off topic i know.
On Aug 25, 2014 1:41 PM, "Jason Szumlanski" <jason at fafcosolar.com<mailto:jason at fafcosolar.com>> wrote:
I had a tough customer recently that grilled me on how we can put a 270W solar module on a 215W inverter. Fortunately, Enphase has a wonderful white paper on the subject. However, it got me thinking... Enphase has demonstrated that higher output panels in many climates (hot SW Florida included) can benefit from modules that far exceed the inverter rating, and even exceed the inverter's "recommended input" rating. Enphase has shown that 270W+ modules can show energy harvest on the M215 where it makes sense to "oversize" the module.

I also received a similar query from a rather uninformed plan reviewer in an area AHJ along similar lines. Fortunately I was within the "recommended input" rating on the spec sheet of 270W with a 265W module, but I wonder what would happen if I had paired the M215 with a 280W module on my plans, which are becoming readily available now in 60 cell modules with 300W modules on the near horizon. I'm pretty sure my plan would have been kicked back for exceeding the manufacturer's recommendation.

My question, which applies to string inverters and microinverters, is how much is too much, what would happen if you paired an array that far exceeded the rating, and how do inverter manufacturers determine the recommended and/or maximum rating of the connected module or array? Also, why do some manufacturers have a simple recommendation while others have a "maximum" rating?


Jason Szumlanski
​Fafco Solar​



_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140826/a329257f/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 332 bytes
Desc: image001.jpg
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140826/a329257f/attachment-0005.jpg>


More information about the RE-wrenches mailing list