Can the Sunny Island be programmed to not transfer to AC2, but only charge batteries?  If so, how is this done?

 

William

 

 

From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Steve Jefferson
Sent: Friday, August 15, 2014 11:11 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] More Sunny Island power problems

 

Afternoon William,

 

The communication is there to send the signal to the Sunny Boys to go into off-grid mode, when the grid fails. 

Frequency shift still occurs when current is not needed from the SBoy’s. 

 

I typically would not recommend that a UPS circuit be placed in the protected loads panel.

The UPS is looking for grid issues, and I think the frequency shift feature would probably fall under that.

 

As for the SI frying the UPS, it is my opinion that the UPS failed. It should have disconnected and started to provide backup power to its loads when the SI started to shift the freq.

That’s its job.

 

I Still think it is a good idea to examine the SI data, maybe you can figure out if the SI was in Freq shift mode when the UPS failed.

 

Thanks 

 

SMA America, LLC

Steve Jefferson

Service Line Supervisor

3925 Atherton Ave

Rocklin, CA 95765 - 3714

U.S.A.

Tel:  +1 916 625 3185 (direct)

Fax: +1 916 625 0871

Mobile: +1 916 622 4253

Email: Steve.jefferson at SMA-America.com

 <http://www.sma-america.com/> www.SMA-America.com

 

 <http://www.youtube.com/watch?v=yQWzPuyqhzo&feature=youtu.be> cid:image001.png at 01CF1CFA.FE18BEB0

 

This email and any attachments thereto may contain SMA America, LLC confidential, privileged and private material for the sole use of the intended recipient. Any review, copying, or distribution of this email (or any attachments thereto) by others is strictly prohibited. If you are not the intended recipient, please contact the sender immediately and permanently delete the original and any copies of this email and any attachments thereto. Thank you.

 

 

 

From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of William Miller
Sent: Friday, August 15, 2014 9:55 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] More Sunny Island power problems

 

Mac:

 

I will review the data.  Thanks!

 

William

 

Gradient Cap_mini
Lic 773985
millersolar.com <http://www.millersolar.com/> 
805-438-5600

 

From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Mac Lewis
Sent: Friday, August 15, 2014 9:46 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] More Sunny Island power problems

 

William, 
As far as I understand, the communication is supposed to take away the need for frequency shift. Have you pulled the data off of the Sim card and looked for frequency shift?

On Aug 15, 2014 10:24 AM, "William Miller" <william at millersolar.com> wrote:

Friends:

 

A Sunny Island mini-grid system I am maintaining also does not play nice with a UPS unit.  So much so that the system reportedly fried a Furman UPS unit yesterday!  

 

This should not be!  The UPS unit is supposed to protect downstream equipment and should be able to protect itself as well.  

 

I need to rent some high quality power monitoring equipment to monitor voltage, frequency and distortion.  I need one three phase unit in the power building and I need something more compact for the AV equipment room.  Does anyone have a recommendation for models that might work in this scenario?

 

The thought occurred to me that the system by which the Sunny Island varies line frequency may be problematic for sensitive electronics.  I have connected the Sunny Island master to the Sunny Boys with RS485 and programmed the Sunny Boys for off-grid.  Can this allow the two systems to communicate to regulate PV charge without relying on frequency shifting?

 

Thanks in advance.

 

William

 

 

Gradient Cap_mini
Lic 773985
millersolar.com <http://www.millersolar.com/> 
805-438-5600

 


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140815/aad2fb61/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 30736 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140815/aad2fb61/attachment-0005.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.jpg
Type: image/jpeg
Size: 1460 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140815/aad2fb61/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.jpg
Type: image/jpeg
Size: 1460 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140815/aad2fb61/attachment-0007.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1461 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140815/aad2fb61/attachment-0008.jpg>


More information about the RE-wrenches mailing list