[RE-wrenches] High specific gravity
Mac Lewis
maclewis1 at gmail.com
Tue Aug 12 20:01:54 PDT 2014
Thanks for the responses everyone. I never considered that acid may have
been added. I'll have to press him a little bit on that. He's definitely
"old school" so I wouldn't be surprised if he tried this. Dan, I
calibrated the refractometer, so I have confidence in its readings. When I
say all over the place, we had 3 cells of specific gravity of 1.0, the rest
ranged from 1.24-1.33. He is going to equalize again, but we will see if
he added acid.
Thanks again.
On Tue, Aug 12, 2014 at 8:13 PM, William Miller <william at millersolar.com>
wrote:
> Mac:
>
> Someone has added acid to the cells. I've had the same experience and
> found out the truth later on.
>
> William
>
> Miller Solar
>
> On Aug 12, 2014, at 6:54 PM, Mac Lewis <maclewis1 at gmail.com> wrote:
>
> Hello wrenches,
>
> I just went on a service call for a new client. He had a bank of 4 year
> old Interstate L16HCL batteries, 2 strings of 8, 48V system, 840Ahr. We
> went through the batteries and got specific gravity on all of the cells
> post-equalization. I was a bit surprised to see some very high numbers ie
> over 1.32 for the specific gravities (higher than my refractometer goes).
> The specific gravities were all over the place, but I haven't seen numbers
> this high. I don't have a great explanation. He has a stacked 3648 VFX
> Outback system, and the set-points were 58.8V Absorb for 2 hours, and 62V
> Equalize for 2 hours. He has a decent amount of solar (about 3400W) and a
> 1000W wind generator.
>
> Any ideas why the specific gravity is so high on some cells? Also, is
> there anything wrong with having SG this high, post-equalization? For this
> very standard battery, what settings do you go with (Bulk, Absorb, Float,
> Eq, and times for Abs and Equalization).
>
> Thanks in advance
>
>
>
> --
>
>
>
> Mac
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
--
Mac Lewis
*"Yo solo sé que no sé nada." -Sócrates*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140812/9de9dec8/attachment-0002.html>
More information about the RE-wrenches
mailing list