Larry Crutcher, Starlight Solar Power Systems larry at starlightsolar.com
Wed Jul 2 11:55:59 PDT 2014


Hi Roy,

The FullRiver DC400-6 AGM battery can issue 2000 amps for 5 seconds so he should be fine.

Larry

On Jul 2, 2014, at 12:35 PM, Roy Butler <roy at four-winds-energy.com> wrote:

I haven't seen anyone mention the battery bank. If I understand correctly, there's a single string of sealed
L16 batteries on this inverter. I have my doubts as to whether or not that bank can provide the high current
the inverter needs to start this load.
Roy Butler
NABCEP Certified Solar PV Installer®
NYSERDA eligible PV & wind installer
IREC Certified Master Trainer™ for Small Wind Installer
Four Winds Renewable Energy, LLC
8902 Route 46, Arkport, NY 14807
607-324-9747  www.four-winds-energy.com

Join us at the 10th Annual Small Wind Conference
A Gathering of Installers, Manufacturers, Dealers, & Distributors
June 17 and 18, 2014 in Stevens Point, Wisconsin
www.smallwindconference.com

Although no trees were killed in the sending of this message, 
a large number of electrons were terribly inconvenienced.

                
On 7/2/2014 2:10 PM, Jason Szumlanski wrote:
> To further qualify my statements, the inverter will start the pump without issue, but I should echo the warnings by others that if there are other loads present, especially other motor loads that could start ​concurrently, you may experience issues. As long as your customer understands the limitations and possibilities, you may be just fine.
> 
> 
> Jason Szumlanski
> ​ Fafco Solar​ 
> 
> 
> 
> On Wed, Jul 2, 2014 at 11:00 AM, Jason Szumlanski <jason at fafcosolar.com> wrote:
> For what it's worth, I've run a single speed 1.5HP pool pump with a MS4448PAE in a mobile application on a 38.4kWh battery bank (sixteen Rolls S-530's). I have also run a 2.5HP Hayward EcoStar Variable Speed pool pump at full RPM, but that startup current is likely less than you well pump.
> 
> I'm going to guess your 3/4HP well pump will be a breeze to start with this inverter.
> 
> 
> Jason Szumlanski 
> ​ Fafco Solar​ 
> 
> 
> On Wed, Jul 2, 2014 at 10:47 AM, Allan Sindelar <allan at sindelarsolar.com> wrote:
> Drake,
> As a normal CYA, I'll always gently let a customer know that this (or any) particular combination of inverter and load sometimes proves incompatible, just in case the unexpected happens. (We once had a MS4448 that would not reliably start and run a condensing boiler; a switch to a different boiler resolved the issue.)
> 
> Having said that note of caution, I wouldn't give it any concern. 3/4 HP and 1 HP well pumps have never been an issue; I would expect 1.5 HP to be easy to run. At 2 HP I'd be asking these questions here. 
> 
> You might check that it's a 3-wire, capacitor-start motor, but nowadays nearly all are. Two-wire pumps (with no control box) can add 50% to the surge.
> 
> The Magnum has a fairly poor voltage regulation response. Sometimes the AC voltage can drop to ~80 VAC momentarily. So you might also caution your customer that the lights may flicker when the pump starts. In our home we know whenever our Kenmore fridge turns on.
> 
> Allan
> 
> Allan Sindelar
> allan at sindelarsolar.com
> NABCEP Certified PV Installation Professional
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> Founder (Retired), Positive Energy, Inc.
> 505 780-2738 cell
> 
> 
>  
> On 7/2/2014 8:17 AM, Drake wrote:
>> Hello Wrenches,
>> 
>> We are hoping to use a Magnum PAE 4448 to back up a household that includes a 3/4 HP deep well pump. There is about 120 feet of vertical rise and about 1000 feet of horizontal distance. 
>> 
>> I have been told that there is a correlation between the locked rotor current of a pump and the predictable ability of a specified inverter to power that pump. 
>> 
>> The plumber who installed the pump left no paperwork and retained no records of what pump he put in the hole last year. He could only say it was a 3/4 HP pump. We are therefore unable to obtain the manufacturer's nameplate specifications.
>> 
>> The Magnum PAE 4448 has a 1 mS surge of 70 A (at 240 V) and a 100 MS surge of 40 A. According to the NEC Table 430.251(A), a 3/4 HP motor has a locked rotor current of 41.4 amps at 230 V. 
>> 
>> This inverter can surge at 35.4 A for 5 seconds. The specified battery bank will be 8 Full River  L-16 AGMs. Can anyone say if:
>> Is there enough information to know if this setup will handle the pump, and if so, will it?
>> How can an inverter's ability to power a motor or pump be calculated by knowing its locked rotor current? Which surge periods should be compared to the locked rotor current?
>> Does the surge current need to equal locked rotor. How long must the inverter meet its required maximum surge?
>> From experience with Magnums and pumps, does this seem like a good combination?
>> 
>> Thank you,
>> 
>> Drake 
>> 
>> Drake Chamberlin
>> Athens Electric LLC
>> OH License 44810
>> CO License 3773
>> NABCEP Certified Solar PV 
>> 740-448-7328
>> http://athens-electric.com/ 
> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140702/77675e33/attachment-0002.html>


More information about the RE-wrenches mailing list