[RE-wrenches] Pv wire

Kirk kirk at vtsolar.com
Thu Jun 26 10:58:17 PDT 2014


Dan,
Pv wire is xlpe.

Kirk Herander
VSE

> On Jun 26, 2014, at 1:44 PM, dan at foxfire-energy.com wrote:
> 
> 
> I got .0437" for RHH-2 with outer jacket in the 2011 code
> 
> -------- Original Message --------
> Subject: [RE-wrenches] Pv wire
> From: "Kirk" <kirk at vtsolar.com>
> Date: Thu, June 26, 2014 1:15 pm
> To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
> 
> Hi folks,
> What is the proper approximate in2  area to use for #10 1kva/2kva  pv wire for calculating conduit fill? I'm on a job site and don't have the specs with me. Thanks.
> 
> Kirk Herander
> VSE
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 



More information about the RE-wrenches mailing list