Thu Jun 26 10:58:17 PDT 2014
Dan,
Pv wire is xlpe.
Kirk Herander
VSE
> On Jun 26, 2014, at 1:44 PM, dan at foxfire-energy.com wrote:
>
>
> I got .0437" for RHH-2 with outer jacket in the 2011 code
>
> -------- Original Message --------
> Subject: [RE-wrenches] Pv wire
> From: "Kirk" <kirk at vtsolar.com>
> Date: Thu, June 26, 2014 1:15 pm
> To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
>
> Hi folks,
> What is the proper approximate in2 area to use for #10 1kva/2kva pv wire for calculating conduit fill? I'm on a job site and don't have the specs with me. Thanks.
>
> Kirk Herander
> VSE
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
More information about the RE-wrenches
mailing list