How are you protecting each inverter separately
On Jun 25, 2014 6:20 PM, "Corey Shalanski" <cshalanski at joule-energy.com>
wrote:

> I am curious about best practices for combining the output of multiple
> inverters:
>
>    - We are considering using an insulated tap "Polaris/Burndy" connector
>    in lieu of a solar accumulation panel. We would then run the output of this
>    tap connector through a fused disconnect and on to the interconnection.
>    Does anyone else do this?
>    - In the above scenario, how should we size the wire between each
>    inverter's output and the tap connector? Since there is no OCPD on this
>    wire, would we have to use the same wire gauge as the combined output? or
>    can we get away with sizing each wire according to its associated inverter
>    output rating?
>
> --
> Corey Shalanski
> Joule Energy
> New Orleans, LA
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140625/370471d8/attachment-0002.html>


More information about the RE-wrenches mailing list