[RE-wrenches] AFCI disturbances. wire nuts

Ray Walters ray at solarray.com
Wed Jun 25 11:01:32 PDT 2014


I've had butt splices fail, due to a ratchet release type crimper that 
didn't pinch the wires tight enough.
I now use a good old Klein crimper that puts a big indent on one side.  
The problem with this however, is that it damages the built in 
insulation.  My favorite butt splice is uninsulated, and then slide 
adhesive shrink wrap up tubing up over the connection after.  We use 
these on submersible pumps that are 100 ft under water with no issues.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 6/25/2014 11:43 AM, Nathan Charles wrote:
> Hi All,
>
> Has anybody had success with these butt splices with the adhesive 
> shrink tubing? http://www.mcmaster.com/#butt-splices/=skb9qs
>
> Best,
>
>
>
> On Wed, Jun 25, 2014 at 1:12 PM, August Goers <august at luminalt.com 
> <mailto:august at luminalt.com>> wrote:
>
>     Hi All -
>
>     We have been using outdoor Ideal brand wire nuts (the blue ones packed
>     with waterproof gel/grease) for all of our residential DC side splices
>     (typically #10 wire) for 10 years now and have never had a single
>     problem.
>     If the installers properly strip the conductors and follow the
>     instructions I feel that these wire nuts make very robust
>     connections. We
>     always do a good pull test after twisting the wire nut on. I would
>     never
>     recommend standard wire nuts without the grease and have seen
>     these fail
>     numerous times during inspections of systems installed by others.
>     Insulated terminal blocks also work well but don't have that nice
>     waterproof grease in them to help avoid moisture issues. You can
>     wrap them
>     with a good splicing tape to help keep moisture out but the cost
>     for these
>     connections is significantly higher than wire nuts:
>
>     http://solutions.3m.com/wps/portal/3M/en_US/EMDCI/Home/Products/Catalog/~?
>     N=5433135&rt=c3
>     <http://solutions.3m.com/wps/portal/3M/en_US/EMDCI/Home/Products/Catalog/%7E?%0AN=5433135&rt=c3>
>
>     Normally I error on the robust conservative side of the installation
>     spectrum but in this case it sounds like I may not.
>
>     Just my $0.02
>
>     Best, August
>
>
>     -----Original Message-----
>     From: RE-wrenches
>     [mailto:re-wrenches-bounces at lists.re-wrenches.org
>     <mailto:re-wrenches-bounces at lists.re-wrenches.org>] On
>     Behalf Of William Miller
>     Sent: Wednesday, June 25, 2014 8:40 AM
>     To: RE-wrenches
>     Subject: Re: [RE-wrenches] AFCI disturbances.
>
>     Richard:
>
>     Possibly. I think I prefer din mount connector blocks. However, if
>     a wire
>     nut can arc internally a connector block might also. I am still
>     wondering
>     about this concept.
>
>     William
>
>     Miller Solar
>
>     > On Jun 25, 2014, at 6:09 AM, Richard.L.Ratico at valley.net
>     <mailto:Richard.L.Ratico at valley.net> (Richard L
>     Ratico) wrote:
>     >
>     > William,
>     > Would UL listed crimp sleeves be an acceptable substitute where you
>     > would otherwise use wirenuts?
>     >
>     > Dick Ratico
>     > Solarwind Electric
>     >
>     >
>     > --- You wrote:
>     > Bob-O:
>     >
>     >
>     >
>     > When you say verboten, what does that mean?  Not kosher?
>      Frowned upon?
>     > Disallowed by law???
>     >
>     >
>     >
>     > I am quite curious about this subject.  Here is what I have
>     learned so
>     far:
>     >
>     >
>     >
>     > This is a unique case where we are replacing 3 dead SMA U series
>     > inverters with 2 US series inverters.  The U series seem to all be
>     > dying at about 12 to 14 years of age.  We have about a dozen of
>     these
>     > to swap on our calendar and expect more.  It may be that to do this
>     > right requires that we pull new wire from the arrays.  This
>     makes the
>     job a lot more expensive.
>     >
>     >
>     >
>     > We have never used a wire nut on a PV lead until this project.  It's
>     > not that we disapprove of wire nuts in general, it is because we
>     know
>     > that if we were to use them regularly we would eventually have
>     failures
>     and call backs.
>     > We allow only one splice in a PV lead: between the cable provided by
>     > the manufacturer of the module and a bulkhead mounted MC4 connector
>     > direct to THWN in conduit
>     >
>     (http://millersolar.com/MillerSolar/practices/PV_wiring/PV_Cable_wirin
>     > g/_PV_
>     > Cable_Wiring.html).
>     >
>     >
>     >
>     > We checked the manufacturer's listing and the wire nuts are
>     rated for
>     > 600 volts.  We do use wire nuts on AC circuits, such as switch and
>     > receptacle circuits in a power room.
>     >
>     >
>     >
>     > A tech at SMA told me that wire nuts "arc internally to the spring"
>     > causing the AFCI faults.  I am not aware of any process of "internal
>     > arcing."  To me, arcing means, as per the dictionary definition: "a
>     > luminous bridge formed in a gap between two electrodes."  The same
>     > tech told me to solder the leads and apply shrink tubing.  I don't
>     > believe this is an approved method.  By the way, we have spliced
>     leads
>     > on both US series inverters and only one is exhibiting AFCI
>     disturbances.
>     >
>     >
>     >
>     > I do favor mounted terminal blocks, either screw or tubular type. I
>     > need to check if the Amp model we stock are 600 volt rated.
>     >
>     >
>     >
>     > I was told by another representative from SMA that on a ground-mount
>     > system it is legal to disable the AFCI protection.
>     >
>     >
>     >
>     > I will be troubleshooting this job tomorrow and I will let you all
>     > know what I learn.
>     >
>     >
>     >
>     > William Miller
>     > --- end of quote ---
>     > _______________________________________________
>     > List sponsored by Redwood Alliance
>     >
>     > List Address: RE-wrenches at lists.re-wrenches.org
>     <mailto:RE-wrenches at lists.re-wrenches.org>
>     >
>     > Change listserver email address & settings:
>     > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>     >
>     > List-Archive:
>     >
>     http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist
>     > .html
>     >
>     > List rules & etiquette:
>     > www.re-wrenches.org/etiquette.htm
>     <http://www.re-wrenches.org/etiquette.htm>
>     >
>     > Check out or update participant bios:
>     > www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>     >
>     _______________________________________________
>     List sponsored by Redwood Alliance
>
>     List Address: RE-wrenches at lists.re-wrenches.org
>     <mailto:RE-wrenches at lists.re-wrenches.org>
>
>     Change listserver email address & settings:
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>     List-Archive:
>     http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.htm
>     l
>
>     List rules & etiquette:
>     www.re-wrenches.org/etiquette.htm
>     <http://www.re-wrenches.org/etiquette.htm>
>
>     Check out or update participant bios:
>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>     _______________________________________________
>     List sponsored by Redwood Alliance
>
>     List Address: RE-wrenches at lists.re-wrenches.org
>     <mailto:RE-wrenches at lists.re-wrenches.org>
>
>     Change listserver email address & settings:
>     http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>     List-Archive:
>     http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>     List rules & etiquette:
>     www.re-wrenches.org/etiquette.htm
>     <http://www.re-wrenches.org/etiquette.htm>
>
>     Check out or update participant bios:
>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
>
> -- 
> Nathan Charles
> Engineer
> NABCEP Certified PV Installation Professional #042013-20
> Paradise Energy Solutions
> (717) 283-2021 direct
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140625/55d5bc8c/attachment-0002.html>


More information about the RE-wrenches mailing list