[RE-wrenches] Charging a HUP

Chris Mason cometenergysystems at gmail.com
Sun Feb 9 10:20:21 PST 2014


A 12KW generator can produce 250A at 48V, and the breaker should be 12KW
*125% or 62.5 amps.
You may have an unbalanced load, you probably can only put 6KW per leg of
the 240V feed.


On Sat, Feb 8, 2014 at 2:46 AM, <bruce at willpowerelect.com> wrote:

> Hi All,
>
> 3 VFX 3648
> 2 FM 80
> 6.5 kw solar
> 12 kw generator
> PSX 240 on generator output and VFX stacking
> Mate 3
> HUP 1690 ah
>
> System design considering 45 amp charge current from each VFX totaling 135
> amps. (135 x ~55v = 7.42kw)  Potential charge current from 2 arrays and FM
> 80's, 90 - 100 amps. On a good day, reasonable to expect 200+ amps?
> Have not been able to exceed 90 amps for more than 30 minutes, with the
> generator putting out about 9 kw before it's 70 amp 2pole breaker trips. L1
> 42 amps, L2 37 amps. 5 amps neutral. Load banked to 12.3 kw (51 amps @
> 240v) resistive without breaker trip.
> I have had to dial back the maximum charge current in the Mate 3 to 12
> amps each on two of the inverters (L1 and L2) and 8 on inverter 3 to keep
> the generator from tripping out when customer turns on the microwave or
> coffee pot. In effect, 42 amps charge @ 240 v = 7.6 kw. At the battery, I'm
> only seeing 80 amps of charge current. Running loads are typically less
> than 1 kw but there has been a of construction going on with chop saws and
> compressors creating annoying spikes that are easily handled by the
> inverters when the generator is off.
> I don't want to kill this new battery by not feeding it properly! I would
> have put in a larger generator, but the owner bought the 12 kw before
> deciding on the new battery. I thought the 12 would be merely adequate, but
> not so....
> Any suggestions?
>
> Thanks!
>
> Bruce Fiero-RMI
>
>
>
>
>
> *"I'd put my money on the sun and solar energy. What a source of power! I
> hope we don't have to wait until oil and coal run out before we tackle
> that." T. Edison, 1931*
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
President, Comet Systems Ltd
www.cometenergysystems.com
Cell: 264.235.5670
Skype: netconcepts
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140209/1bae4b92/attachment-0004.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: sigimg0
Type: image/jpeg
Size: 3467 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140209/1bae4b92/attachment-0004.jpe>


More information about the RE-wrenches mailing list