I agree that Voc doesn't seem to degrade as much. I've had a chance to
measure several modules over 20 years old, and the Voc is only dropping
about 1/2 the rate suggested by others here. I think a more
appropriate number might be 0.25% V drop/ year.
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 6/4/2014 11:36 AM, Nathan Charles wrote:
> So I read this paper, Smith, R. M., Jordan, D. C., & Kurtz, S. R.
> (2012). Outdoor PV Module Degradation of Current-Voltage Parameters,
> which seems to seems to suggest that Voc doesn't degrade like Isc
> degrades. Based on that and other data I've seen it seems like panels
> that degrade at 0.5%/year are outliers on the low side.
>
> Thoughts from other wrenches?
>
>
>
>
> On Tue, Jun 3, 2014 at 11:59 PM, Bill Hoffer <sunengser at gmail.com
> <mailto:sunengser at gmail.com>> wrote:
>
> Dana
>
> Bill Brooks, passed on past data, ( correct me Bill if I am out of
> date here) recommends 1% Power loss per year with approximately
> 0.5% current and 0.5%voltage. That is also what Solar Energy
> International Best Practices curriculum recommends. Based on some
> newer data from larger projects requiring testing to actually
> determine those values for the Bankability requirements ( PVsyst
> PAN files), I believe we are seeing lower numbers than that now.
> In general, quality of modules are higher than the older modules.
> We of course are usually not privy to those results and may not
> even be getting the same level of binning for small residential
> projects as the MW projects do. 0.5% V loss per year seems like
> a like a good conservative number to me, especially if you add a
> little buffer (1-2%) in there.
>
> Bill
>
>
> On Tue, Jun 3, 2014 at 3:41 PM, Dana Brandt
> <dana at ecotechenergy.com <mailto:dana at ecotechenergy.com>> wrote:
>
> Hi Wrenches,
>
> Does anyone know what percentage of module degradation over
> time is voltage and what is current? I'm wanting to make sure
> we give ourselves plenty of breathing room on the minimum Vmp
> of the inverters over the long term so need to try to
> anticipate how much voltage we'll lose on the array over 30
> years.
>
> Thanks,
>
> Dana
>
> Dana Brandt
> Ecotech Energy Systems, LLC
> www.ecotechenergy.com <http://www.ecotechenergy.com>
> dana at ecotechenergy.com <mailto:dana at ecotechenergy.com>
> 360.318.7646 <tel:360.318.7646>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
> <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
>
>
> --
> William Hoffer
> 161 SE Fourth Ave
> P.O. Box 1823
> White Salmon, WA 98672-1823
> sunengser at gmail.com <mailto:bhoffer at sunergyengineeringservices.com>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
> <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
>
>
> --
> Nathan Charles
> Engineer
> NABCEP Certified PV Installation Professional #042013-20
> Paradise Energy Solutions
> (717) 283-2021 direct
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140604/de82c3ec/attachment-0003.html>
More information about the RE-wrenches
mailing list