[RE-wrenches] 2014 NEC
jay peltz
jay at asis.com
Tue May 20 08:10:12 PDT 2014
HI Will,
You can do this.
Take a standard breaker panel, install a Arc fault and run the wiring from the enphase like it is the grid: ie into the main lugs.
Then this will go out through the breaker in the correct fashion, and onto the main panel.
jay
peltz power
PS as to the code, they want it this way
On May 20, 2014, at 7:59 AM, Will White wrote:
> Wrenches,
>
> Is anyone else having problems with inspectors and the 2014 NEC? In Mass we’re having all kinds of issues with inspectors requiring/allowing an array of different things for 690.12 rapid shut down ranging from roof top disconnects, disconnects on the side of a house 20’ up, disconnects in attics, or only disconnects that can be activated on the ground. It varies between inspectors.
>
> We’re also having problems with one inspector requiring arc fault breakers on Enphase even though there are no UL listed arc fault breakers that can be back fed or he wants us to run the trunk cable in a raceway.
>
> It’s getting very difficult to install in Mass.
>
> Thanks,
> Will
>
> Will White
> Operations Manager - New England
> RGS Energy
> 64 Main St. |Montpelier, VT 05602
> tel 802.223.7804 | mobile 802.234.3167 | fax 802.223.8980
> RGSEnergy.com | william.white at rgsenergy.com
>
>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20140520/2e029b7f/attachment-0003.html>
More information about the RE-wrenches
mailing list